Hacking an APC 1400UPS by adding external batteries for a Matrix Battery Pa

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Hacking an APC 1400UPS by adding external batteries for a Matrix Battery Pa
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:50 AM

0 Likes
2
2855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:50 AM

Hacking an APC 1400UPS by adding external batteries for a Matrix Battery Pa

Hi,

I recently get a used APC 1400XL UPS (no power modules installed).

I need to use this a long haul UPS when the power goes out (2-5 hours on a 700W) load.

I may also have access to a Matrix UPS battery pack which I believe is also 48V and was thinking of using it with this UPS.

Any thoughts?

Note I have two sources for a Matrix UPS Battery Pack: -- see attached pics:
1. Matrix.JPG - options 1
2. matrix-battery-option-2-.png, matrix-battery-option-2-.png - option 2

Thanks.

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:50 AM

0 Likes
0
2855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:50 AM

The 1400 xl unit has 2 batteries inside witch mean it works on 24 volt dc,you can be more sure by checking inside unit battery quantity and measuring the voltage on the external batteries connectors.
if you need to connect your matrix battery pack you need to reconfigure the battery connection to get the right voltage.
but take in consideration that once you add an external battery to apc unit you have to configure the unit software by the right number of external battery pack quantity,
it is essential because other wise the charger will not deliver more amps to charge battery in a fast time.you can configure the battery number with powerchute program.
you can send me the battery specification on matrix unit and i will calculate to you the righ number you have to enter on the software.
one more thing there is a limit of battery capacity that you can add to the apc unit.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Javik_apc
Lieutenant JG Javik_apc
Lieutenant JG

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:50 AM

0 Likes
0
2855
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:50 AM

I don't work for APC but generally the company spokespeople are going to say "buy our battery packs" and "we won't warantee hacking projects".

I will point you to my own battery hacking guide:
Referenced content removed

The items about correct voltage are especially important here. Symmetras may run at a significantly different battery voltage from the Smart-UPS, and you may blow up the UPS circuitry or fry the batteries, up to and including boiling the acid and exploding the vented hydrogen gas.

Proceed very cautiously.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:50 AM

0 Likes
0
2856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:12 AM . Last Modified: ‎2024-03-08 04:50 AM

The 1400 xl unit has 2 batteries inside witch mean it works on 24 volt dc,you can be more sure by checking inside unit battery quantity and measuring the voltage on the external batteries connectors.
if you need to connect your matrix battery pack you need to reconfigure the battery connection to get the right voltage.
but take in consideration that once you add an external battery to apc unit you have to configure the unit software by the right number of external battery pack quantity,
it is essential because other wise the charger will not deliver more amps to charge battery in a fast time.you can configure the battery number with powerchute program.
you can send me the battery specification on matrix unit and i will calculate to you the righ number you have to enter on the software.
one more thing there is a limit of battery capacity that you can add to the apc unit.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.