rate of change issues causes battery discharge on smt1500

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • rate of change issues causes battery discharge on smt1500
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
143
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:53 AM

0 Likes
3
2137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:53 AM

rate of change issues causes battery discharge on smt1500

I have been having weird issues for the last few weeks.

The outlet my UPS was plugged into (also has a brother laser printer plugged into it) has been having issues where the UPS would making clicking and buzzing like it was handling small power change and the printer would reboot (the printer was not connected to the UPS).

This has been happening since i got the printer a few weeks ago.

Last night the UPS turned itself off because th batter was drained.  The 4 lights were going in sequence.  I have an NMC.

I let the battery charge, and connected the printer to the UPS.  All was well.

This morning all equipment was off again, battery was drained, UPS was flashing in sequence the 4 lights.  The UPS was going through restart loops every 60 seconds, batter did not appear to have charged.  I cancelled the restart, batter is now charging.

I have a Brultech GEM electricity monitor it indicated voltage varies between 119.6 and 122.6, it only polls once a minute, variance seems low.

I am going to take the printer offline the in case that is affect this.  

  1. why does the battery not recharge itself before the UPS attempts to turn on?
  2. what could be causing this?
  3. why did it log nothing to my syslog server (test works)

help!?

--edit-- event.txt attached - why is the darn log so small?

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:53 AM

0 Likes
0
2135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:53 AM

To close the thread.  I moved the printer to a different wall socket on the same circuit and the issue has gone away (no impact to the UPS) the printer is still randomly rebooting, so i will go talk to them next.

Thanks for folks help!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:53 AM

0 Likes
0
2135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:53 AM

Hi,

Sounds like the laser printer is drawing enough energy to cause the UPS to see a drop in voltage and causing the UPS to switch to battery. When a print is sent to a laser printer the printer must warm up. During this warm up process inherently the printer draws a grater than average amount of energy called inrush. Your description indicates the inrush is great enough to case the UPS to switch to battery.

I am assuming the printer and UPS are plugged into a standard 15 amp circuit? You should check the printer specifications to see if it requires something greater. You should also check to see what the inrush (initial draw) of the printer is. Even if rated for 15 amps if it is drawing close to max 80 percent of the 15 amps (12 amps) it could be over loading the circuit and causing the systems to power down.  

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:53 AM

0 Likes
0
2135
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:53 AM

Thanks Bill, the issue occurs s when it is sitting at 'ready' it draws 70W according to the spec.

Yes this is on normal household circuit, luckily i have an energy monitoring solution, that monitors and aggregates the light and power circuits. I have attached the last 4 weeks of watts over time, some things to note:

  • the regular looking daily bump is lights being turned on by home automation
  • the printer has been on network since 10/12 or there about - with no change to what it is doing (sits idle most of the time)
  • the spikes in week 3 and week 4 getting increasing in frequency with no uptick in printing or new equipment
  • I was out in EMEA for last week of oct / first two weeks of November
  • the spikes to 900 watts IMO occurred at same time as the UPS (without printer in it) would make noises and at the same time the printer we would reboot and re-initialize
  • as such i think the spike might be the printer initializing after each weird event (its why i put the printer on the UPS i assumed that the outlet was having issue) i assumed the printer initializing was symptom not cause....

Amps never exceeded about 5 to 6 amps over that time.

edit--- i guess what i am saying is the printer and ups was in steady state and then issue started with no obvious change i can put my finger on.... i am going to leave the printer unplugged for 48 hours and see if the issue disappears, then i will try bringing it back on a different circuit in the house, then a different socket on the study power circuit.

For reference:

http://support.brother.com/g/b/spec.aspx?c=eu_ot〈=en∏=mfcl8900cdw_all

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:53 AM

0 Likes
0
2136
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:05 AM . Last Modified: ‎2024-03-18 12:53 AM

To close the thread.  I moved the printer to a different wall socket on the same circuit and the issue has gone away (no impact to the UPS) the printer is still randomly rebooting, so i will go talk to them next.

Thanks for folks help!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore