Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

"time on battery" reported incorrectly

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • "time on battery" reported incorrectly
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:03 AM . Last Modified: ‎2024-03-06 02:11 AM

0 Likes
7
2488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:03 AM . Last Modified: ‎2024-03-06 02:11 AM

"time on battery" reported incorrectly

the attached screenshot says it all...

I have not had 7 days worth of outages.

I did a self test and it says it's fine....

is my ups ok? or is it the software that's a little wonky?

thank you very much for your assistance!

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • back-ups
  • communication
  • management
  • PowerChute
  • usb
  • windows
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 01:04 AM . Last Modified: ‎2024-03-06 02:10 AM

0 Likes
0
2488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:04 AM . Last Modified: ‎2024-03-06 02:10 AM

its 3.0.0.1

also if there is no way to reset the data would you please pass the suggestion to the developers of the software to include that in the next version?

That would be excellent!

Message was edited by: agnxnetworks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:03 AM . Last Modified: ‎2024-03-06 02:11 AM

0 Likes
0
2488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:03 AM . Last Modified: ‎2024-03-06 02:11 AM

silly question but hear me out - may i ask how you have not had 7 days of outages within a 4 week timeframe? keep in mind it can transfer to battery in the middle of the night or for power fluctuations, not necessarily when the power goes out completely.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:03 AM . Last Modified: ‎2024-03-06 02:11 AM

0 Likes
0
2488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:03 AM . Last Modified: ‎2024-03-06 02:11 AM

I've had the unit since dec 19th.

if this is really true then we have more power events then I thought!

but the thing is if the outage happened my husband's computer is not on a UPS and it was still on.

wierd....

I never thought our power quality was that bad though. I have it at medium sensitivity

voltages are set up at 88 at the low end and 139 on the high end.

I just really wanna make sure this is not a bug in the software.

Thank you very much for the reply!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:03 AM . Last Modified: ‎2024-03-06 02:11 AM

0 Likes
0
2488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:03 AM . Last Modified: ‎2024-03-06 02:11 AM

ahh i see..can you reset the data and see if it does it again? if so, then we look further. i agree, it seems unlikely that if you have another computer that doesnt turn off, your UPS probably didnt go to battery but it could be possible if the voltage just dipped low and your UPS went on battery to get you closer to 120v versus a lower value of 75 or something. some PC power supplies might be able to handle the lower voltage and not turn off - i am not 100% sure.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:04 AM . Last Modified: ‎2024-03-06 02:11 AM

0 Likes
0
2488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:04 AM . Last Modified: ‎2024-03-06 02:11 AM

how do i reset the data?

do I shut down the service and delete the log file? or can I just stop the datasrv.exe process and delete the log file?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:04 AM . Last Modified: ‎2024-03-06 02:11 AM

0 Likes
0
2488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:04 AM . Last Modified: ‎2024-03-06 02:11 AM

also I am having extreme HDD activity with datasrv.exe as well!

800 some page fault delta.....

I killed that process does it have any ill effects???

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:04 AM . Last Modified: ‎2024-03-06 02:10 AM

0 Likes
0
2488
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:04 AM . Last Modified: ‎2024-03-06 02:10 AM

honestly, i didnt look and thought there was an option to reset the data.

also, datasrv is the process that deals with energy usage. what version of PCPE are you using? this would be listed under the About section on the left - we fixed some "noisy drive" issues in 3.0.0.1 so if you are using 3.0, we can try 3.0.0.1 to see if that is what you are hearing. if you have to upgrade to 3.0.0.1, that will reset the data. if not, let me know and ill see if there is any other way to manually reset the data. i honestly thought there was a button to clear it, my apologies.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 01:04 AM . Last Modified: ‎2024-03-06 02:10 AM

0 Likes
0
2489
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 01:04 AM . Last Modified: ‎2024-03-06 02:10 AM

its 3.0.0.1

also if there is no way to reset the data would you please pass the suggestion to the developers of the software to include that in the next version?

That would be excellent!

Message was edited by: agnxnetworks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore