"UPS: The output power is turned off due to a low battery."

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • "UPS: The output power is turned off due to a low battery."
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-12 04:28 AM

0 Likes
3
1539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-12 04:28 AM

"UPS: The output power is turned off due to a low battery."

Hi,

I am seeing a red "replace battery" light on my Smart-UPS RT 10000 XL. The unit actually power cycled yesterday morning with the messages in bold (the date is obviously wrong = 11/09/2002= Jan 6 2014.

11/09/200206:35:42UPS: The output power is now turned on.
11/09/200206:35:38UPS: The output power is turned off due to a low battery.
10/31/200220:32:36UPS: Failed a self-test.
10/17/200220:33:20UPS: Failed a self-test.
10/17/200220:33:05UPS: At least one faulty battery exists.
10/17/200220:33:04UPS: A faulty battery no longer exists

Obviously it's my priority to replace the batteries. Why would it power cycle though? Do I run the risk of this happening again before I can get batteries replaced? As I understand it the replacement batteries come in twos, so I would need 2xRBC44 to replace the batteries in the "Battery Pack", is that correct?


IF i want to determine which of the batteries is bad, should I remove one RBC44 and perform a self-test? This system is critical and I'd much rather just replace all batteries, thus avoiding down time. That should be possible?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-12 04:28 AM

0 Likes
0
1539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-12 04:28 AM

Hello again.

Yes, you're right - the default setting is every two weeks for a self test but that can be modified. You'd see that option under Diagnostics in your Network Management Card.

If you just have "SURT10000XLT" then you just need qty (2) RBC44 which are the physical (4) strings that go inside the UPS itself. Sounds like since today is 11/9 according to your log, that the next self test would be around the 13th of November in your log..? (I am bad at math - lol embarassed)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-12 04:28 AM

0 Likes
0
1539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-12 04:28 AM

If the batteries are very far gone (AKA "toast"), it is feasible that the output turned off during the self test. In your data log, what does the battery voltage show - normally and during the self test period? A self test failure/replace battery indicator normally should give you about a month's leeway before the batteries fail but factors can affect that (ambient temperature, battery health/quality, other environmental factors, etc) so this is not typical for it to drop a load after a self test in most circumstances.

And the SURT10000XLI or SURT10000XLT both take qty (2) RBC44 as you suggested for the UPS itself. If you have any SURT192XLP's with it, they also take qty (2) RBC44 each (per Buy APC Smart-UPS RT 192V Battery Pack - Technical Specifications and Information | APC). It is always recommended to replace all of the batteries at the same time if they are the same age. This UPS cannot identify individual strings that are faulty anyway so it is telling you to replace the (2) RBC44's. Putting new RBC44's with old RBC44's would damage the newer ones too - bad batteries typically damage new ones if put on to the same bus.

Hope that helps. Let me know if you have further questions or need clarification. I'd recommend replacing all the RBC44's ASAP to avoid further issues during the next self test or during a power event.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-12 04:28 AM

0 Likes
0
1539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-12 04:28 AM

Hi,

Thanks for the quick reply. The last self test was 10/31, but I seen no indication of one yesterday. As I understand it, it self tests every two weeks?

Battery voltage shows:

Battery
Capacity:100.0 %
Battery Voltage:216.0 VDC
External Batteries:1

My entire unit looks like this - http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SURT10000XLT - thus I do not have any other SURT192XLP's right? I just have the 2xRBC44's that come in the "Battery Pack" part of the unit as you can see on the link. Or is there also RBC44's inside the actual UPS too?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-12 04:28 AM

0 Likes
0
1540
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 07:26 AM . Last Modified: ‎2024-03-12 04:28 AM

Hello again.

Yes, you're right - the default setting is every two weeks for a self test but that can be modified. You'd see that option under Diagnostics in your Network Management Card.

If you just have "SURT10000XLT" then you just need qty (2) RBC44 which are the physical (4) strings that go inside the UPS itself. Sounds like since today is 11/9 according to your log, that the next self test would be around the 13th of November in your log..? (I am bad at math - lol embarassed)

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of