Hi,
we have an APC SMART-UPS 1500VA LCD (SMT1500) with UPS 05.0 (ID17) firmware and AP9630 (HW revision 05) NMC2 installed.
It was running
Mr6bwPGBLXRp%2BRRRg54mmw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg
I upgraded to v6.2.0:
jv3v6q7FMcx4Fm6cwHqRmA%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.jpeg
...but now the NMC2 reports "No UPS Found". Please help.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:40 PM . Last Modified: 2024-03-14 04:13 AM
This is just a case of choosing the wrong firmware application by mistake (note on v6.1.1 the "sumx" application for Smart-UPS in use under Application Module in your screenshot and "sy" for Symmetra UPSs on 6.2.0). You just need to download the correct firmware and re-apply it the same way you did the wrong firmware originally. Look for part number SFSUMX620 on the website under http://www.apc.com/tools/download/index.cfm after you select Firmware Upgrades - UPS Network Management Card under Filter by Software/Firmware. Once you re-run that upgrade, you'll be good to go.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:40 PM . Last Modified: 2024-03-14 04:13 AM
This is just a case of choosing the wrong firmware application by mistake (note on v6.1.1 the "sumx" application for Smart-UPS in use under Application Module in your screenshot and "sy" for Symmetra UPSs on 6.2.0). You just need to download the correct firmware and re-apply it the same way you did the wrong firmware originally. Look for part number SFSUMX620 on the website under http://www.apc.com/tools/download/index.cfm after you select Firmware Upgrades - UPS Network Management Card under Filter by Software/Firmware. Once you re-run that upgrade, you'll be good to go.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:40 PM . Last Modified: 2024-03-14 04:13 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:40 PM . Last Modified: 2024-03-14 04:13 AM
Thank you! Problem solved.
BTW: Do you know if the USV firmware (UPS 05.0 (ID17)) is current? I searched the forum/net but it is hard to find an answer.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:40 PM . Last Modified: 2024-03-14 04:13 AM
It looks like there is a new update for your UPS per this article -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA164737
You can also get the right firmware and use your Network Management Card to push the update to your UPS -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA170679
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:40 PM . Last Modified: 2024-03-14 04:13 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:40 PM . Last Modified: 2024-03-14 04:13 AM
Angela, thank you again for your help.
I updated our UPS to v07.1 without any problems through the NMC.
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:41 PM . Last Modified: 2024-03-14 04:13 AM
You're very welcome! ![]()