new OID

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • new OID
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

0 Likes
3
2681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

new OID

Hello, sorry for my english.

Can i find somewhere info for new OID 1.3.6.1.4.1.318.1.4 tree ? Everywhere is caled as experimental.

1.3.6.1.4.1.318.1.4.2.2.1 and last .6, .8, .10 , .11, .12, 13

This tree looks like a HW inventory UPS and card AP9631 in. With serial number hw type and version...

and

1.3.6.1.4.1.318.1.4.2.4.1 looks like SW version for sn ...

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • experimental
  • number
  • oid
  • serial
  • snmp
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

0 Likes
0
2681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

Hi again Tomáš,

Try this OID: .1.3.6.1.2.1.1.1 (.iso.org.dod.internet.mgmt.mib-2.system.sysDescr) the output looks like this from my AP9631:

APC Web/SNMP Management Card (MB:v4.1.0 PF:v6.4.6 PN:apc_hw05_aos_646.bin AF1:v6.4.6 AN1:apc_hw05_sumx_646.bin MN:AP9631 HR:05 SN: ZA15XXXXXX MD:05/14/2015) (Embedded PowerNet SNMP Agent SW v2.2 compatible)

I've highlighted some key bits of information including AOS version, application version, model number, and serial number. Can you use this? It is what we would typically recommend for a good summary of the NMC hardware's details.

*Edit* I forgot to add, if you are also in need of the UPS firmware/hardware versions (or whatever device type the NMC is installed in), that information lives inside the different device/product subtree. So for example, if it is a UPS, you'll find it contained within some OIDs under iso(1).org(3).dod(6).internet(1).private(4).enterprises(1).apc(318).products(1).hardware(1).ups(1)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

0 Likes
0
2681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

Hi Tomáš

1.3.6.1.4.1.318.1.4 is not intended for customers. It is an 'experimental' tree and OIDs for APC use only. You may see some responses here but they are for internal applications, like StruxureWare Data Center Expert.

The values you see returned there are available for the most part in other areas of the SNMP MIB intended for our users. Which values/information are you looking for? We could help provide you the correct OIDs that you, as a user, should be looking for.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

0 Likes
0
2681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

Hello.
Thanks for answer.
In my free time make one my application, where training my brain with programing :).

I now search some inventory OID tree with HW and SW version all components,
becouse 1.3.6.1.2.1.47.1.1.1.1 (ENTITY-MIB) from AP9631 not works.

But when i look on all 1.3.6.1 tree output of this card, than not view some another OID with HW info tree.
For exaple serial number management card is only in experimental OID or in main 1.3.6.1.2.1.1.1.0.
Or is some hidden tree with inventory component's?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

0 Likes
0
2682
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

Hi again Tomáš,

Try this OID: .1.3.6.1.2.1.1.1 (.iso.org.dod.internet.mgmt.mib-2.system.sysDescr) the output looks like this from my AP9631:

APC Web/SNMP Management Card (MB:v4.1.0 PF:v6.4.6 PN:apc_hw05_aos_646.bin AF1:v6.4.6 AN1:apc_hw05_sumx_646.bin MN:AP9631 HR:05 SN: ZA15XXXXXX MD:05/14/2015) (Embedded PowerNet SNMP Agent SW v2.2 compatible)

I've highlighted some key bits of information including AOS version, application version, model number, and serial number. Can you use this? It is what we would typically recommend for a good summary of the NMC hardware's details.

*Edit* I forgot to add, if you are also in need of the UPS firmware/hardware versions (or whatever device type the NMC is installed in), that information lives inside the different device/product subtree. So for example, if it is a UPS, you'll find it contained within some OIDs under iso(1).org(3).dod(6).internet(1).private(4).enterprises(1).apc(318).products(1).hardware(1).ups(1)

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of