Setting up a Smart UPS 10000 for generator backup

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Setting up a Smart UPS 10000 for generator backup
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:35 PM

0 Likes
31
4532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:35 PM

Setting up a Smart UPS 10000 for generator backup

I have set up an automated transfer switch so that if there is a power loss, a generator will kick in.

In testing, I could see 240VAC and around 63HZ yet the UPS would not use the power and instead stayed on batteries even though there was power.

The generator puts out 30AMPS and the load is only 15AMPS. There was plenty of time for the UPS to accept the generator power but it didn't.

What reason would it do that? The second light below the utility light was on and it stayed on batteries until it died.

Help... please! smile

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

0 Likes
0
4531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

All of this still tells me bad batteries. In a perfect world, it would be obvious and I know it is annoying that the UPS is not actually lasting for the reported runtime but depending on the type of battery failure, it is possible the replace battery LED does not show or that beyond a certain amount of usage of the batteries per outage, that the runtime just drops off. The reported runtime while online is a really good estimate and when it switches to battery is when it is able to calculate it a lot better.

My recommendation here to address this is to replace both RBC44 in the UPS. If I look at the runtime chart, (UPS Runtime Charts) even at half load on SURT10000XLT you should be getting closer to 15 minutes, nevermind the 16-30% load that showes in your data log. The other thing that would be nice to know that I don't recall currently is how long it actually lasts on battery. If we go by what just happened, let's say that's about 2-3 minutes. It'd be a different issue if it lasted 20 minutes but only reported 5.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 31
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:35 PM

0 Likes
0
4526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:35 PM

Can you get me the full event.txt and data.txt logs from this time period? I need the data.txt to look at at least to compare to what you just posted.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:35 PM

0 Likes
0
4526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:35 PM

I have put them both online. Do you still have the URL I gave you or do you want me to post it for a moment?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:34 PM

0 Likes
0
4526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:34 PM

I have it. The issue I see is no matter if I go to /event.txt or /data.txt, I am only seeing the event.txt file and no data log. I also might as well ask - no changes recently in shutdown settings right? I looked at your old config.ini and I will go off of that assuming you did not change the low battery duration value.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:34 PM

0 Likes
0
4525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:34 PM

I must have jumbled something up. Try again, I've reuploaded everything smile.

And no, haven't changed any settings. My assumption is batteries need to be changed, as we discussed before. Just weird that it held the load no problem, only losing one LED of the five, then the next time, didn't even hold the load for a moment.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

0 Likes
0
4526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

Well, I'd definitely start with the management card logs and reviewing them from your testing time.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

0 Likes
0
4526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

I looked and there wasn't anything much other than the UPS saying 'UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.'. But, that was the error before anyhow.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

0 Likes
0
4526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

I think I'll have to start from scratch again.

My concern is that testing is killing the batteries which aren't great to start with.

I'd like to be able to test in a way that puts the load on battery long enough to see if the UPS would take the genset power or not then back to utility.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

0 Likes
0
4526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

Could I take a look at the log files? If you want to post them, can you tell me what time/dates to reference during the test?

I believe you are familiar with the log file download but here are instructions if you need it-> http://www.apc.com/support/index?page=content&country=US〈=en&id=FA156131

I am also interested in the [SmartUPS/Matrix] version of the config.ini to see what the thresholds for voltage/frequency are set to.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

0 Likes
0
4526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

You can pick up the config.ini at /config.ini

You can pick up the log at /apc.log

Please let me know once done and I will delete them.

Please let me know if this is what you need.

The testing would have been on the 28th and 29th I believe. You can tell because the dns servers went missing when everything went down.

The 28th might actually be the test date because I see;

07/28/201323:36:17System: Coldstart.
07/28/201323:25:53UPS: The output power is turned off.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

0 Likes
0
4526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

The instructions I sent show you how to FTP in to the NMC and you get config.ini, data.txt and event.txt. Then you can select "use advanced editor" in the reply box and attach the files there.

I need to look at the data log and event log at the same time. Event log alone (that you provided) doesn't answer all of my questions cry

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

0 Likes
0
4526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

Hardware Factory
Model Number:AP9619
Serial Number:ZA0443007046
Hardware Revision:A10
Manufacture Date:10/21/2004
MAC Address:00 C0 B7 71 0E A6
Management Uptime:9 Days 16 Hours 7 Minutes
Application Module
Name:sumx
Version:v3.5.8
Date:11/05/2008
Time:15:08:57
APC OS (AOS)
Name:aos
Version:v3.6.1
Date:08/13/2008
Time:18:49:49

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

0 Likes
0
4527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

Same url, only /data.txt and /event.txt

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

0 Likes
0
4527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

I got event.txt and data.txt but I just cannot get to config.ini at the URL. You can remove them as I downloaded and saved them.

I am focusing on the 28th/29th but now I just need to verify the threshold settings via the config.ini for frequency and voltage to see if the problem was that even though it was not too far out of tolerance in your opinion from the generator, that the UPS setting was too restrictive.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

0 Likes
0
4527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:27 AM . Last Modified: ‎2024-03-12 11:32 PM

Oops, thought you got that one already so had deleted it. It's back now smile

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

0 Likes
0
4527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

I have since been working on the generator which seems to have developed a problem. It doesn't appear to be putting out 240VAC anymore so I might have a voltage controller problem.

I did have a meter on it when I was testing and it was putting out 240VAC but it's possible that it showed that briefly while I was looking then might not have been.

Once you see the details, you might be able to tell me if my UPS settings are ok at least. They were not changed from the previous setup which was with a genset also but maybe resetting the card and powering off, etc, changed some settings.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

0 Likes
0
4527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

Thanks! I also consulted my Smart UPS RT counterpart in escalation for some input. You can remove those files now.

Here are our observations:

  • You only have 30% load on the UPS so you might be able to get away with a smaller sized generator but ideally, it'd be a 30kVA generator. (what size is it?) If that was the issue, it could be Total Harmonic Distortion on the input to the UPS but I know you've already mentioned potential generator issues but see point # 2.
  • We did not see anything change between input on AC and generator as far as voltage/frequency.
  • In the config.ini, your output frequency threshold is set to auto which basically says that the UPS will try to match the input frequency to output frequency. You could try adjusting it to 60Hz -/+ 3 Hz for testing as well but we don't believe it will make a huge difference but it is worth a shot.
  • Other than that, not too much we can do overall because it is already a Double Online Conversion UPS and is designed to work with a varying range of input. No other issues with anything we found in the log files.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

0 Likes
0
4527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

I am buying a new generator so I will update this thread once I have received and installed it and am ready to test again.

I hope you'll continue to help me once I have those things in place. I am extremely eager to get this working because I've lost two expensive storage devices thanks to power failures in the last couple of months.

Thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

0 Likes
0
4527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

Yes.. I am sure I'll be here smile

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

0 Likes
0
4527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

>You only have 30% load on the UPS so you might be able to get away with a smaller sized generator but ideally, it'd be a 30kVA generator.

That sounds very wrong. In the previous server room, the amperage being used was more like 25amps at a higher load on same UPS. I had a 16KW NG genset which kept the load up without a problem. At one point, we had the load on the genset for over 24hrs and there wasn't one single blip.

>In this case, (what size is it?) If that was the issue,

The new configuration uses a lot more virtualization so I was able to downsize a lot of the hardware and am now using 12amps to 14amps average at 30% load.

The genset I have now is a 7KW putting out 30amps at full load so I can't see it having a problem with this size load.

>it could be Total Harmonic Distortion on the input to the UPS but I know you've already mentioned potential generator issues but see point

Right, that's what I am thinking. I did make sure the genset was putting out 240VAC at 60hz when I was testing but a while into testing, I started to see the voltage being wrong. Further testing seemed to show new problems with the genset. I have a new one on order which should be here next week.

>Other than that, not too much we can do overall because it is already a Double Online Conversion UPS and is designed to work with a

>varying range of input. No other issues with anything we found in the log files.

So it might have and probably was the genset going bad then? Once I have the new machine connected, tested and ready to go, I'll post just before testing so that we have a fresh start. I can't afford any more outages because they are ruining some expensive storage devices. The batteries seem to hold the load long enough to get to genset so I'll deal with the batteries once the generator is in place.

I am very thankful for your help and input on this!!!


Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

0 Likes
0
4526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

You're welcome. The generator size recommendation of 30kVA was based on 3 times the full capacity of your UPS which is typically our recommendation for this UPS type. You'd probably be fine with at least 1.5 times though.

We'll have to see on the generator but I'd have to say probably because we don't see anything else wrong at this time.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

0 Likes
0
4525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

It should arrive on the 20th so if there's any luck, it will be installed that day or over the next two days then I'll update this thread.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

0 Likes
0
4525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

Yes, everything I am being told seems like it is bad batteries. How old are they again? From going back to your previous posts, this UPS has (2) RBC44 and each RBC44 is (4) "trays." From what I read, previously, you only replaced (1) RBC44 or (2) trays? Is that right? I am asking because since you only replaced half, the batteries try to equalize and the older ones could've destroyed the RBC44 replacement you had done 1.5 years ago (according to the old post I found from June). Did I misunderstand? Your thoughts?

Regardless, the UPS should've indicated a bad battery but sometimes it happens randomly like this if there is an issue that a self test cannot detect or if the event happens before the self test.

What was the runtime reported now after all of this happen? I know the issue when you had 3 minutes reported..wondering if its back around there?

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

0 Likes
0
4526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

And that is what is so confusing. I don't want to spend the money just yet if I don't have to.

The unit tells me I have 5 minutes of run time which would be plenty for a genset fail over. I was on batteries \for only about two minutes I think while changing the breaker and only one LED down from full battery. Then when I tried it again, it turned itself off almost instantly. So it almost seems like it's not registering the right amount of battery power to begin with.

Input Voltage:247.6 VAC
Output Voltage:209.4 VAC
Runtime Remaining:                                                    5 minutes
Last Battery Transfer:Unacceptable utility voltage rate of change

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

0 Likes
0
4526
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:31 PM

Runtime still shows 5 minutes.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

0 Likes
0
4532
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

All of this still tells me bad batteries. In a perfect world, it would be obvious and I know it is annoying that the UPS is not actually lasting for the reported runtime but depending on the type of battery failure, it is possible the replace battery LED does not show or that beyond a certain amount of usage of the batteries per outage, that the runtime just drops off. The reported runtime while online is a really good estimate and when it switches to battery is when it is able to calculate it a lot better.

My recommendation here to address this is to replace both RBC44 in the UPS. If I look at the runtime chart, (UPS Runtime Charts) even at half load on SURT10000XLT you should be getting closer to 15 minutes, nevermind the 16-30% load that showes in your data log. The other thing that would be nice to know that I don't recall currently is how long it actually lasts on battery. If we go by what just happened, let's say that's about 2-3 minutes. It'd be a different issue if it lasted 20 minutes but only reported 5.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

0 Likes
0
4525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

Alright, so I guess I'll have to budget for batteries and then make sure the UPS is reset to fresh batteries.

You didn't see anything in the settings which sounded too off so I'll use the same settings I have now but reset the batteries timer.

Thanks very much for everything on this. It is very much appreciated.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

0 Likes
0
4525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

No problem! Glad to help. Settings looked fine as you mentioned. I'll be here if you need anything else laughing

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

0 Likes
0
4525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

I have set up an automated transfer switch so that if there is a power loss, a generator will kick in.

In testing, I could see 240VAC and around 63HZ yet the UPS would not use the power and instead stayed on batteries even though there was power.

The generator puts out 30AMPS and the load is only 15AMPS. There was plenty of time for the UPS to accept the generator power but it didn't.

What reason would it do that? The second light below the utility light was on and it stayed on batteries until it died.

Help... please! smile

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

0 Likes
0
4525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

Hi mlewis

So just to be clear, you saw the on battery LED on, correct? See screenshot below.

1332_surt10k.jpg

That is the on battery LED with Online above it and bypass is below it so I just want to ensure you did not mean bypass because then we'd have to find out why it was in bypass.

Were you able to check the management card logs at all? I know that this UPS should accept +/- 5Hz if I am not mistaken...

Event and data log may help tremendously though to better understand why it was on battery.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

0 Likes
0
4525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:28 AM . Last Modified: ‎2024-03-12 11:30 PM

Unfortunately, I'm going to have to get on this next week, I'm simply out of time. Yes, it's that LED.

Thanks. I'll get on this when I get back.

Reply

Link copied. Please paste this link to share this article on your social media post.

mlewis_apc
Lt. Commander mlewis_apc
Lt. Commander

Posted: ‎2021-06-29 06:29 AM . Last Modified: ‎2024-03-12 11:30 PM

0 Likes
0
4525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:29 AM . Last Modified: ‎2024-03-12 11:30 PM

Ok, back from our trip and ready to tackle this. Badly need to get the UPS and the genset to work together so any help is very welcome!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore