mge galaxy 3500/Smart UPS VT battery question

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • mge galaxy 3500/Smart UPS VT battery question
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
karbonphiber_apc
Lieutenant JG karbonphiber_apc
Lieutenant JG

Posted: ‎2021-06-26 05:10 AM . Last Modified: ‎2024-03-19 01:05 AM

0 Likes
6
1569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:10 AM . Last Modified: ‎2024-03-19 01:05 AM

mge galaxy 3500/Smart UPS VT battery question

So someone told me that the mge galaxy 3500/Smart UPS VT cannot be used with higher AH, 10 year design life batteries without a good reason. I think this person is full of s**t and I suspect that they can be, but that they cannot be used concurrently with the smaller 7.2Ah, internal batteries due to the battery charger circuit's inability to provide equalized charging to two different sized battery strings.

Can anyone attest to using higher Ah batteries on the mge galaxy 3500/Smart UPS VT?

Message was edited by: karbonphiber

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:05 AM

0 Likes
0
1569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:05 AM

Yes, you could connect a third party battery plant to the SUVT.
As mentioned in another post on the same topic; you will gain run-time, but the battery plant will be unmanaged.
There are commercially available battery plants with the correct configuration.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:10 AM . Last Modified: ‎2024-03-19 01:05 AM

0 Likes
0
1569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:10 AM . Last Modified: ‎2024-03-19 01:05 AM

Hi,

1. Information:

First, this UPS can work with external 3rd battery. But how much Amp it's depend on the battery charged (size of UPS), if you put too much, after UPS restart to charge the battery, the charger may be blown down.

Typical 100Ah (C20 is ok). You will see each smart battery module (4 set per module) = 7.2Ahr and they can connect up to 4 external smart battery cabinet(6 module per cabinnet). So max may be 7.2Ahr*6*4 Ah is the maximum support for this UPS.

2. Connection :

You look at the back side of UPS and will see the terminal with BAT +, BAT - and common battery (Ground).

So the connection should be + 0 - (3 wire) and you can use 32 to 34 battery block 12V per string.
Please get the correct wiring size to prevent : DC voltage drop < 1% (if cable lenght > 15m) and support largest current. Refere to install manual.

3. Configuration
You need declar Ampe hours (@C20 parameter) for your battery system to UPS.

You go to menu Setup/other.

Key the Amper hours to UPS.

Do a selftest action.


Keep the battery full charged and do the calibration in control menu with 25% load. Its' will make the UPS display runtime correct.

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 05:10 AM . Last Modified: ‎2024-03-19 01:05 AM

0 Likes
0
1569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:10 AM . Last Modified: ‎2024-03-19 01:05 AM

No you cannot use the SYBTU2 batteries which is the new higher AH rated battery in the Symmetra PX/SUVT/3500. These UPS use the SYBTU1 battery. The same is also true that you cannot use the old SYBTU1in the PX500 and PX100, both of these use the new SYBTU2. The good reason is because you can't and they won't work.

I wouldn't be too concerned with the battery lifetime difference either. The expected lifetime of the SYBTU2 battery is very similar to the SYBTU1 5-8 years.

http://www.apcmedia.com/salestools/BMOE-7PDSSB_R1_EN.pdf

So for a recap

Symmetra PX 20-40-80(not sure if on PX's outside of NAM), SUVT, Galaxy 3500 : SYBTU1 7.2AH batt
Symmetra PX100 - PX250/500 : SYBTU2 9ah

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:10 AM . Last Modified: ‎2024-03-19 01:05 AM

0 Likes
0
1569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:10 AM . Last Modified: ‎2024-03-19 01:05 AM

Jason,

There are, among others, physical considerations of using the higher Ah battery with SUVT. The battery cartridge simply won't fit; it's bigger than the cabinet is designer to accept.

From a theoretical standpoint you probably could use just about any battery with similar charging characteristics. As it is, adding parallel strings to the SUVT produces a battery plant with a higher overall Ah rating.
In practice the SYBT4 battery string is going to be the most cost effective.

Reply

Link copied. Please paste this link to share this article on your social media post.

karbonphiber_apc
Lieutenant JG karbonphiber_apc
Lieutenant JG

Posted: ‎2021-06-26 05:10 AM . Last Modified: ‎2024-03-19 01:05 AM

0 Likes
0
1569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:10 AM . Last Modified: ‎2024-03-19 01:05 AM

upsguy, mfitzsimmons - thanks for your responses but sorry, let me qualify my what I am asking here. Could I use an MGE Galaxy 3500 or Smart UPS VT with a 3rd party battery system that is designed with the appropriate number of battery blocks (32 blocks with a neutral connection), 100Ah batteries, appropriate sized DC, 3p breaker, and connect it to the external battery input terminals on the UPS system?

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-26 05:10 AM . Last Modified: ‎2024-03-19 01:05 AM

0 Likes
0
1569
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:10 AM . Last Modified: ‎2024-03-19 01:05 AM

I've found the mention of external Large AH batteries being able to be used with these UPS and there is a menu option for external AH rating. I'm still looking as to how the controls would be connected to the UPS though. Will get back once I've found a better answer.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:05 AM

0 Likes
0
1570
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 05:11 AM . Last Modified: ‎2024-03-19 01:05 AM

Yes, you could connect a third party battery plant to the SUVT.
As mentioned in another post on the same topic; you will gain run-time, but the battery plant will be unmanaged.
There are commercially available battery plants with the correct configuration.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of