low Runtime Remaining Smart-UPS RT 8000 XL

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • low Runtime Remaining Smart-UPS RT 8000 XL
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

0 Likes
10
3342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

low Runtime Remaining Smart-UPS RT 8000 XL

Hi There

We have a low run time remaining of  11min

Here are the other value given :

The load of the server isn't much about 16% but I only have   11  remaining which I think should be a lot more then that ??

I did a calibration test but still the remaining minutes are still the same can you help?

thanks 

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 8000
  • rt
  • smart-ups
  • xl
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:29 AM

0 Likes
0
3342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:29 AM

I just called scheider electric and they are gonne send me new battery ( again) those i received might be a bad set so once i received it i will gave them 24h charges and let you know if that fix my problem, thanks for the help 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

0 Likes
0
3342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

Hello Sir,


Good day to you. There are few reason why you will encounter such problem. You can reference to this article:

http://www.apc.com/us/en/faqs/FA157077/.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

0 Likes
0
3342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

thanks for the reply

so you say if

Light load accuracy- The estimated runtime values quoted on the web are based on an algorithm which tends to be less accurate for light loads and long runtime applications.

my load is too loght  the ups will be less accurate ? so i should put some more  load to it ??

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

0 Likes
0
3342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

That would be one thing we you can try. Also have you ever replaced the batteries of the UPS? If you did, when was the last time?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:30 AM

0 Likes
0
3342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:30 AM

I just try to add some more loads but the minutes are decreasing to 6   min !!!

I change the battery in 2012-06-01

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:29 AM

0 Likes
0
3342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:29 AM

I have ordered a new sets of battery wich i change and still i have 11 min left with 16% load , can you help please ????

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:29 AM

0 Likes
0
3342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:29 AM

can anybody help please ????

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:29 AM

0 Likes
0
3342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:29 AM

Did you perform a runtime calibration on the new battery?

After the battery has charged for 8 hours, I would unplug the UPS and see how long it runs your load. We'll call that "actual runtime." Then let it recharge and compare the actual runtime with the new estimate. I would also try comparing with the advertised runtime for the SRT8000XL, but I don't see the specs on APC's website anymore.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:29 AM

0 Likes
0
3342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:29 AM

yes i did full calibration and self test with the new battery  still with the load at 20% i have 5 min left 

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:29 AM

0 Likes
0
3342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:29 AM

Alright. It'll be interesting to see how that 5 minute estimate compares to the actual runtime.

You might also want to inspect the battery for any serial numbers that could indicate date of manufacture.

Also, if the replacement is a genuine APC battery, you could contact APC's tech support here:

http://www.apc.com/us/en/support/contact-us/

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:29 AM

0 Likes
0
3343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:16 PM . Last Modified: ‎2024-03-07 12:29 AM

I just called scheider electric and they are gonne send me new battery ( again) those i received might be a bad set so once i received it i will gave them 24h charges and let you know if that fix my problem, thanks for the help 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore