Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Output Load threshold Exceeded on Smart-UPS 3000

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Output Load threshold Exceeded on Smart-UPS 3000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

0 Likes
6
3715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

Output Load threshold Exceeded on Smart-UPS 3000

Twice in past 48 hours unit has shutdown.  Events Log claims cause is "Output Load Threshold Exceeded" and "Insufficient Runtime Available" and "Overload", but Data Log seems to show normal numbers, so I'm puzzled.  Attached devices have not changed for at least 12 months.  Logs are attached.  Please advise.

Model = SUA3000l

Serial = JS0602017319 (first character might be "U")

Batteries replaced October 2014 and are rarely needed, and then only for short periods like tripped breakers.

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • overload
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

0 Likes
0
3715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

Hi,

The log shows that both low battery and overload occurred so that is why the system powered down. The data log does not show the event but that most likely is because the data log is set to only capture every 20 minutes so the event/s were missed.  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

0 Likes
0
3715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

Hi,

What version of PowerChute Business Edition Agent is installed and do you have the PowerChute Business Edition Server and Console installed? 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

0 Likes
0
3715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

Thank you for your reply.

Smart-UPS Firmware Revision = 655.12.I

Agent version = 9.0.3.604

Host is Hyper-V 2008 Core.  Only Agent is installed on host.  Server and Console were not installed, but I have just now installed them on a Hyper-V Guest.  Status is green.  Ran reports and got following results:

Risk Assessment > only warning is UPS Age.

Voltage Analysis > 240-247.  

Power Event Analysis > No data.

Power Event Summary > No data.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

0 Likes
0
3715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

Hi,

The power event summaries would not show anything since the PowerChute Server had just been installed. The PowerChute web Agent event log showed the events lasting for a few seconds so that could be why the data log is not recording the issue. The data log appears to be set to record every 20 minutes which is the default setting. 

In the web interface how do you have PowerChute configured? What events are set to trigger a system shut down?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

0 Likes
0
3715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

Hi,

The following events are configured to trigger shutdown:

Communication Lost While On Battery

UPS Internal Temperature Threshold Exceeded

Low Battery

Overload

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

0 Likes
0
3715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

Hi Bill,

Any ideas?

Thanks, Richard

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

0 Likes
0
3716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 08:15 PM . Last Modified: ‎2024-03-07 12:30 AM

Hi,

The log shows that both low battery and overload occurred so that is why the system powered down. The data log does not show the event but that most likely is because the data log is set to only capture every 20 minutes so the event/s were missed.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore