Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
looking for auto/scheduled start up of UPS and computer feature...?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3005:29 AM. Last Modified: 2024-03-0802:29 AM
The way this needs to work is that the UPS has to be responsible for a graceful unattended shutdown. Once complete the UPS will go into a low voltage sleep mode waiting for utility power to return. Meanwhile, your equipment's PSU is waiting for power to return to IT so it can turn back on. Keep in mind that for this to work, you must setup your BIOS so that the "Last State" or whatever it may be called, is set to ON. You may want to contact your vendor to configure this.
Once input power is restored to the UPS, it will cycle power to itself by going online, back to on battery, then back online, which will in essence, turn the outlets on the UPS back on providing power to your equipment. If you want a more controlled outlet by outlet scenario, you may want to look at a Modular UPS, or integrating a switched rack PDU which will allow for turn on delays and such.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3005:29 AM. Last Modified: 2024-03-0802:29 AM
The way this needs to work is that the UPS has to be responsible for a graceful unattended shutdown. Once complete the UPS will go into a low voltage sleep mode waiting for utility power to return. Meanwhile, your equipment's PSU is waiting for power to return to IT so it can turn back on. Keep in mind that for this to work, you must setup your BIOS so that the "Last State" or whatever it may be called, is set to ON. You may want to contact your vendor to configure this.
Once input power is restored to the UPS, it will cycle power to itself by going online, back to on battery, then back online, which will in essence, turn the outlets on the UPS back on providing power to your equipment. If you want a more controlled outlet by outlet scenario, you may want to look at a Modular UPS, or integrating a switched rack PDU which will allow for turn on delays and such.