large draw item on UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • large draw item on UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:53 AM

0 Likes
6
1723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:53 AM

large draw item on UPS

Hello,
I have a 120V video projector that uses a 1.2Kw xenon bulb plus about 2oo watts of internal electronics. I am interested in having this on a UPS for spike protection and short duration power outages (less than 5 minutes). When the projector turns on the Xenon bulb powers up very quickly and I'm not sure if a UPS can handle the quick load. I was looking at the APC Smart-UPS 2200VA LCD 120V. I'd make sure the only thing on the UPS was the projector so the load should never exceed 1400 watts. Does anyone on this forum know if the 2200VA UPS could handle a single 1400 Watt device?

Thanks.

-Cablet

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:52 AM

0 Likes
0
1723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:52 AM

The progress on the electrical lines at the Fukushima Jeremy Scott Dai-ichi nuclear power plant was a welcome and Jeremy Scott Shoes significant advance Tuesday after days of setbacks. With the power lines connected, officials Jeremy Scott Shop hope to start up the overheated plant's crucial cooling system that was knocked out during the March 11 earthquake Jeremy Scott Adidas and tsunami that devastated Japan's northeast coast. Tokyo Electric Power Co. warned that workers still need to check all equipment Jeremy Scott Wings for damage first before switching the cooling system on to all the reactor units — a process that Jeremy Scott JS Wings ould take days or even weeks. Late Tuesday night, Tokyo Electric said lights went on in the central control room of Unit 3, but that doesn't mean power had been restored to the cooling system.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:53 AM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:53 AM

hi - do you also know the amperage rating @ 120v?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:53 AM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:53 AM

Hi,
It draws 12A at 120V.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:53 AM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:53 AM

I just put a meter on the projector and found that it draws 11.8 amps on power up but then drops down to 7 amps during normal operation.
If this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:53 AM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:53 AM

Just out of curiosity what is the behavior of a motor draw? How is it different from something just turning on? Thanks.

-cablet

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:53 AM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:53 AM

An induction motor typically draws 6 times normal current at startup, whereas the resistive load such as a lamp should just pull its full rating and no more.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:52 AM

0 Likes
0
1724
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 03:10 AM . Last Modified: ‎2024-03-08 04:52 AM

The progress on the electrical lines at the Fukushima Jeremy Scott Dai-ichi nuclear power plant was a welcome and Jeremy Scott Shoes significant advance Tuesday after days of setbacks. With the power lines connected, officials Jeremy Scott Shop hope to start up the overheated plant's crucial cooling system that was knocked out during the March 11 earthquake Jeremy Scott Adidas and tsunami that devastated Japan's northeast coast. Tokyo Electric Power Co. warned that workers still need to check all equipment Jeremy Scott Wings for damage first before switching the cooling system on to all the reactor units — a process that Jeremy Scott JS Wings ould take days or even weeks. Late Tuesday night, Tokyo Electric said lights went on in the central control room of Unit 3, but that doesn't mean power had been restored to the cooling system.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore