SU2200INET trim LED always on after battery replacement

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SU2200INET trim LED always on after battery replacement
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 03:10 AM . Last Modified: โ€Ž2024-03-08 04:52 AM

0 Likes
4
922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 03:10 AM . Last Modified: โ€Ž2024-03-08 04:52 AM

SU2200INET trim LED always on after battery replacement

I have two SU2200INET SmartUPSs which have slightly different firmware.
* The test UPS has serial number YS0321110227, firmware 100.14.M
* The control UPS (where nothing is wrong) has serial number YS0336222267, firmware 80.14.I
The test UPS's batteries were over seven years old and failed suddenly. They overheated and warped slightly, and a very small amount of battery gel escaped and corroded the terminal bolts. The batteries were replaced by an authorized APC service company.

The problem: Ever since the battery replacement, the amber "trim" LED is permanently on.

To our knowledge nothing has changed about utility power. The control UPS is behaving fine.

Apart from this LED behavior and low output voltage, the test UPS is doing fine, including self-tests.

h2. Test UPS

Upper transfer voltage HITRANSFER 239 229 234 239 224
Lower transfer voltage LOTRANSFER 177 177 172 168 182
Return threshold RETURNCHARGE 15 00 15 50 90
Output voltage on batts OUTPUTVOLTS 208 208
{color:#ff0000}MODEL : SMART-UPS *1400*{color}
STATUS : TRIM ONLINE
LINEV : 231.4 Volts
MAXLINEV : 232.7 Volts
{color:#ff0000}OUTPUTV : 205.4 Volts{color}
SENSE : Low
LOTRANS : 177.0 Volts
HITRANS : 239.0 Volts

h2. Control UPS

Upper transfer voltage HITRANSFER 253 253 264 271 280
Lower transfer voltage LOTRANSFER 196 196 188 208 204
Return threshold RETURNCHARGE 0 00 15 50 90
Output voltage on batts OUTPUTVOLTS 230 230 240 220 225
MODEL : SMART-UPS 2200
STATUS : ONLINE
LINEV : 231.4 Volts
MAXLINEV : 232.7 Volts
OUTPUTV : 231.4 Volts
SENSE : High
LOTRANS : 196.0 Volts
HITRANS : 253.0 Volts


Questions:
* Why is the UPS model wrong on the test UPS?
* Why are the programmable values for low and high transfers different?
* Is there something we can do to make the test UPS behave like the control UPS?
Thanks for any advice.

Message was edited by: soumen@cse.iitb.ac.in

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • led
  • su2200inet
  • trim
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 03:11 AM . Last Modified: โ€Ž2024-03-08 04:52 AM

0 Likes
0
922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 03:11 AM . Last Modified: โ€Ž2024-03-08 04:52 AM

The technician did not (just) modify the battery replacement date. As a battery ages, the UPS changes its estimate of the drain and charge capacities and rates. When the battery is at the end of its service life, the UPS has a fairly poor impression of it. When you connect new batteries, unless some of these stale calibrations are reset, the UPS continues to have a very pessimistic view of the new batteries, even after a runtime calibration. I have witnessed change of batteries for a dozen APC UPSs in my organization, and in each case the technician used a serial console to tell the UPS that it has brand new batteries. Then they charge the new battery to 100% and finally conduct a drain runtime calibration.

I don't see why techniques to fix problems in out-of-warranty APC UPSs cannot be posted on an APC Website. I would very strongly advise anyone against trying to use the same technique to change their model number from the correct one to an incorrect one. There is a grave risk of fire and battery meltdown. I am lucky the mistake made by our technician did not fry our UPS in the first place. So in principle, my postings could prevent a fire, save property and even lives.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 03:11 AM . Last Modified: โ€Ž2024-03-08 04:52 AM

0 Likes
0
922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 03:11 AM . Last Modified: โ€Ž2024-03-08 04:52 AM

Was the printed circuit board maybe bumped when the batteries were installed?

Very unlikely. The terminals and fuses on the kaput batteries were slightly corroded. No gel had contacted any part of the UPS. The old batteries were removed easily. The technician cleaned the terminal lugs and used new bolts and fuses on the new batteries.

Was someone issuing commands to the UPS via the console cable?

Yes. The technician said he reset the battery runtime estimate so that the UPS can calibrate it again. After recalibration over the next few hours, the number reported was very plausible given the load.

Supposing the console commands messed up something else in EPROM (such as telling the UPS it is a US model), how can I fix it?

Thanks a lot.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 03:11 AM . Last Modified: โ€Ž2024-03-08 04:52 AM

0 Likes
0
922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 03:11 AM . Last Modified: โ€Ž2024-03-08 04:52 AM

Turns out the technician had accidentally changed the model code while resetting the battery calibration. I managed to set things right using information on this link:

http://osdir.com/ml/monitoring.nut.user/2007-01/msg00120.html

The steps are (voids warranties!) ---

Open a serial console to the UPS.
Press *1*, wait 2 seconds, press *1* again.
You should see response PROG.
Now press b.
You will see some firmware code.
Keep pressing +* followed by a 1 second pause followed by b until you see the correct firmware code.
That was *80.14.I* for my UPS.
Finally press R to get back to dumb mode.
You should see response BYE or some such.
Quit the console without resetting the serial port in any way.

Once again, do the above at your own risk. No warranties, no indemnity.

Reply

Link copied. Please paste this link to share this article on your social media post.

Javik_apc
Lieutenant JG Javik_apc
Lieutenant JG

Posted: โ€Ž2021-06-30 03:11 AM . Last Modified: โ€Ž2024-03-08 04:52 AM

0 Likes
0
922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 03:11 AM . Last Modified: โ€Ž2024-03-08 04:52 AM

Well,. that was a very interesting read. Sort of like learning how to make a phone "blue box", I guess.

So you can make one UPS act like another by merely changing the model version, and the circuitry actually has the capability of complying with these code changes? Hmm, I suppose I could save some money by buying a 700 and making it think it is a 3000, and tacking on a few marine batteries.. ๐Ÿ˜‰

Next questions:

* Is it bad form to link to an article on hacking the Smart Signalling protocol, on APC's own website? Might as well post jailbreak articles on Apple's forums.

* Why would this "tech" have needed to fiddle with such deep voodoo to reset the battery replacement date? You don't need to go to such extremes for this. Both the normal serial console and web console would work fine for it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: โ€Ž2021-06-30 03:11 AM . Last Modified: โ€Ž2024-03-08 04:52 AM

0 Likes
0
923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2021-06-30 03:11 AM . Last Modified: โ€Ž2024-03-08 04:52 AM

The technician did not (just) modify the battery replacement date. As a battery ages, the UPS changes its estimate of the drain and charge capacities and rates. When the battery is at the end of its service life, the UPS has a fairly poor impression of it. When you connect new batteries, unless some of these stale calibrations are reset, the UPS continues to have a very pessimistic view of the new batteries, even after a runtime calibration. I have witnessed change of batteries for a dozen APC UPSs in my organization, and in each case the technician used a serial console to tell the UPS that it has brand new batteries. Then they charge the new battery to 100% and finally conduct a drain runtime calibration.

I don't see why techniques to fix problems in out-of-warranty APC UPSs cannot be posted on an APC Website. I would very strongly advise anyone against trying to use the same technique to change their model number from the correct one to an incorrect one. There is a grave risk of fire and battery meltdown. I am lucky the mistake made by our technician did not fry our UPS in the first place. So in principle, my postings could prevent a fire, save property and even lives.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of