Posted: 2021-07-08 12:04 AM
This was originally posted on APC forums on 3/20/2015
Trying to setup notification for multiple sites and would like to use Gmail as an smtp server
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:04 AM
This reply was originally posted by Anonymous on APC forums on 3/23/2015
Hi Danny,
PCBE v9.1.1 only supports basic email authentication. It does not support TLS/SSL authentication. At the moment when using PCBE, you will have to use a mail relay and relay the mail to a server over port 25 with plain text email authentication (or no authentication) and then have that server forward it to the actual mail server with SSL/TLS authentication over the port you want.
PCBE 9.2 will have the ability to support TLS/SSL and also changing the port from 25. I have no official date as to when this version will be released.
Regards,
B
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 12:04 AM
This reply was originally posted by Anonymous on APC forums on 3/23/2015
Hi Danny,
PCBE v9.1.1 only supports basic email authentication. It does not support TLS/SSL authentication. At the moment when using PCBE, you will have to use a mail relay and relay the mail to a server over port 25 with plain text email authentication (or no authentication) and then have that server forward it to the actual mail server with SSL/TLS authentication over the port you want.
PCBE 9.2 will have the ability to support TLS/SSL and also changing the port from 25. I have no official date as to when this version will be released.
Regards,
B