APC UPS Data Center & Enterprise Solutions Forum
Schneider Electric support forum for our Data Center and Business Power UPS, UPS Accessories, Software, Services, and associated commercial products designed to share knowledge, installation, and configuration.
Posted: 2021-07-08 12:04 AM
This was originally posted on APC forums on 3/20/2015
Trying to setup notification for multiple sites and would like to use Gmail as an smtp server
Posted: 2021-07-08 12:04 AM
This reply was originally posted by Anonymous on APC forums on 3/23/2015
Hi Danny,
PCBE v9.1.1 only supports basic email authentication. It does not support TLS/SSL authentication. At the moment when using PCBE, you will have to use a mail relay and relay the mail to a server over port 25 with plain text email authentication (or no authentication) and then have that server forward it to the actual mail server with SSL/TLS authentication over the port you want.
PCBE 9.2 will have the ability to support TLS/SSL and also changing the port from 25. I have no official date as to when this version will be released.
Regards,
B
Posted: 2021-07-08 12:04 AM
This reply was originally posted by Anonymous on APC forums on 3/23/2015
Hi Danny,
PCBE v9.1.1 only supports basic email authentication. It does not support TLS/SSL authentication. At the moment when using PCBE, you will have to use a mail relay and relay the mail to a server over port 25 with plain text email authentication (or no authentication) and then have that server forward it to the actual mail server with SSL/TLS authentication over the port you want.
PCBE 9.2 will have the ability to support TLS/SSL and also changing the port from 25. I have no official date as to when this version will be released.
Regards,
B
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.