internal hardware fault - need to replace unit?
  • internal hardware fault - need to replace unit?
network-team
network-team
Cadet
Posted: ‎2023-04-10 05:37 AM
Good morning:
We have a Smart-UPS SRT 5000 that reported an internal hardware fault. Much later, the fault reported as cleared, but the outlet groups were shut off unexpectedly.  This caused a service interruption which we must avoid.
  1. Can you advise what might have caused this?
  2. Do you recommend that this unit be replaced?
Thank you very much for your consideration.
Best regards,
  Tom Krauss
  (posted via network-external@jumptrading.com my team email)
Specifics on incident:
INITIAL REPORT IN LOG
03/05/2023        16:35:26 Device   UPS: An inverter fault exists.       0x0165
03/05/2023        16:35:25 Device   UPS: In bypass in response to an internal hardware fault.         0x011B
3+ WEEKS LATER, DEVICE CLEARED THIS STATE BUT POWER WAS SHUT DOWN
NOTE – there was no action from us, the UPS turned off power on its own
03/31/2023         21:55:22               Device  UPS: The power for switched outlet group 2, Outlet Group 2, is now turned off.         0x0135
03/31/2023         21:55:22               Device  UPS: The power for switched outlet group 1, Outlet Group 1, is now turned off.         0x0135
03/31/2023         21:55:21               Device  UPS: Switched outlet group 2, Outlet Group 2, has been commanded to turn off, sequenced. 0x0174
03/31/2023         21:55:21               Device  UPS: Switched outlet group 1, Outlet Group 1, has been commanded to turn off, sequenced. 0x0174
03/31/2023         21:55:21               Device  UPS: The output power is turned off.      0x0114
03/31/2023         21:55:21               Device  UPS: The graceful shutdown period has ended.  0x014F
03/31/2023         21:55:21               Device  UPS: Return from bypass, internal hardware fault no longer present.                0x01B2
Replies 0