SC620 Just Died All of A Sudden

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SC620 Just Died All of A Sudden
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:28 AM

0 Likes
5
2636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:28 AM

SC620 Just Died All of A Sudden

We have two SC620s that were installed at the same time with our POS system.  Both have literally been on for the same time, same hours, same days, same conditions, etc.

We own several different types of businesses and have APC units going back to 2000s so we know the product and insist on it because they always do the job.

Except that one of the SC620s just all of a sudden died--no lights, no breaker, no beeps--nothing!  I was off site so I couldn't put my hands on it until today, and it's definitely just not responding at all.

I read how to remove the batteries, but it's really in there snug.  Besides removing the battery and giving it power, any other diagnostic advice?  The unit is just maybe 2 years old now.  First time we've had a failure like this.

Any assistance appreciated.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:27 AM

0 Likes
0
2636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:27 AM

Just got the battery out--it was in there so tightly that it took 30 minutes with two screwdrivers to pry it out.  But once it was out it looked like the normal thing we see with spent batteries--swelling on the case.  I checked the precise usage time of this particular unit and it's almost exactly 3 years, so this is to be expected.  I'll get an RBC4 ordered right away.  Thank you!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:27 AM

0 Likes
0
2636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:27 AM

Hi,

If the battery is swollen that indicates the battery failed and has over charged. You should unplug the UPS from the AC source and let it site for 24 hours. After the wait time if the battery can be remove you can swap the old battery for a new one and put the UPS back into service. If the battery cannot be removed after the wait time then the entire UPS should be replaced. 

Reply

Link copied. Please paste this link to share this article on your social media post.

SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:27 AM

0 Likes
0
2636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:27 AM

Thank you Bill.  I've almost never been able to get out a battery without it being somewhat stuck, even after days of sitting.  I'll get this battery out and swap in the battery from the known working one to completely eliminate the UPS itself.

A couple of questions though--why would this have happened? (UPS issue?) and should the unit power on when I finally get the battery out?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:27 AM

0 Likes
1
2637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:27 AM

Hi,

Normally it is a battery issue. When one of the cells in the battery dies the other cells absorb the energy that cell should have causing them to swell and heat up. Occasionally it is a charger fault but 98 percent of the time it is the battery.

On 1/7/2016 9:38 AM, Samir said:

should the unit power on when I finally get the battery out?

 Yes once the battery is good the UPS should power up. 

Reply

Link copied. Please paste this link to share this article on your social media post.

SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:27 AM

0 Likes
0
2637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 10:56 PM . Last Modified: ‎2024-03-06 03:27 AM

Just got the battery out--it was in there so tightly that it took 30 minutes with two screwdrivers to pry it out.  But once it was out it looked like the normal thing we see with spent batteries--swelling on the case.  I checked the precise usage time of this particular unit and it's almost exactly 3 years, so this is to be expected.  I'll get an RBC4 ordered right away.  Thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

SamirD_apc
Lieutenant SamirD_apc
Lieutenant

Posted: ‎2023-04-10 11:55 AM

In response to BillP
0 Likes
0
1930
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-10 11:55 AM

As a followup, battery replacement got the unit back in service.  Have replaced the battery in this unit one more time and the other unit once as well.  They're still doing their job. 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore