Hello all,
I am trying to set up a .fwl file to import to a NMC to only allow traffic to let say, 192.168.1.12 but I'm not sure of the proper syntax to use. I was able to ftp in and pull the "example.fwl" file as a reference. Does anyone have any experience with this?
Thanks in advance,
Rahman
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:53 AM . Last Modified: 2024-03-13 01:16 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:53 AM . Last Modified: 2024-03-13 01:16 AM
Thank You Nicole! I'll give this a try.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:53 AM . Last Modified: 2024-03-13 01:16 AM
Hi Rahman,
Here is an explanation of the proper syntax for a .fwl file:
priority (number), destination host|range|subnet ip|FQDN|any (port), source host|range|subnet ip|FQDN|any (port), protocol any|tcp|udp|icmp|icmpv6, action allow|discard (log)
Here is an example of how you might allow examplehost.example.com all access:
priority 1, destination any, source host examplehost.example.com, protocol any, action allow
Regards,
Nicole
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:53 AM . Last Modified: 2024-03-13 01:16 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:53 AM . Last Modified: 2024-03-13 01:16 AM
Thank You Nicole! I'll give this a try.