I would like to know if it is possible to wire this with a plug input instead of hardwiring. Any help would be greatly appreciated. Thank you in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:52 AM . Last Modified: 2024-03-13 01:16 AM
no problem. 🙂
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:52 AM . Last Modified: 2024-03-13 01:17 AM
hi erin,
we don't sell this with a plug option but you'd need to refer to the local code in the area where this is going to be installed to make sure it is acceptable to use a plug for this UPS (which I guess requires a 50A breaker/plug if I remember correctly). as long as the UPS gets 2 phases, neutral, and a ground, you can add a plug (by a qualified electrician).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:52 AM . Last Modified: 2024-03-13 01:17 AM
well, you'd be de-rating this 50A UPS to a 30A UPS if you use L14-30. so if it is clear that this is now a 30A UPS, and everyone (electrician/code) says its OK, i don't see why not. if the upstream breaker (which should then be 30A) keeps tripping, they might be loading the UPS too much since it can potentially do 50A max.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:52 AM . Last Modified: 2024-03-13 01:16 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:52 AM . Last Modified: 2024-03-13 01:16 AM
So, I can use a plug type L14-30 with this, as long as electrical code and electrician say its ok, correct?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:52 AM . Last Modified: 2024-03-13 01:16 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:52 AM . Last Modified: 2024-03-13 01:16 AM
So, what I really need is a 50 amp plug to go with what the unit breaker is, so not to derate the machine. I just told the guy to get with his electrician, and sent him the specs of the unit wiring so they can work it out, but I think if he is going to have a "plug", instead of the hard-wire, that is what he needs. I appreciate the input on this, very helpful.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:52 AM . Last Modified: 2024-03-13 01:16 AM
no problem. 🙂