firmware upgrade problem
  • firmware upgrade problem
5060
143
petlar930
petlar930
Cadet
Posted: ‎2024-11-13 03:44 AM
429
Hi, we have two SMT2200IC that doesn't want to upgrade via the smartconnect portal, why is that? See attached picture. They are connected to the portal and online.
Kirk
Posted: ‎2024-11-13 08:15 AM . Last Modified: ‎2024-11-14 09:04 AM
The firmware will fail if the following conditions exist:
- Active faults / errors present
- Battery is not at the required level
- Self Test / Battery calibration is running
- High temperature conditions
- Output: Some models the output must be off to allow a firmware update
- Network: It goes without saying any firewall, antivirus, network shaping must be reviewed.
NOTE: There were several instances where different APC Models at a lower firmware version had to be powered down to allow the firmware to be loaded.
Once these units were at the latest revision they could be updated without turning off the outputs or shutting down the system. ☝️
Contact APC Technical Support to see if this issue applies to you. Lastly, the Smart Connect portal has seen service issues. 🤦‍♂️
APC Resource FAQ: https://community.se.com/t5/Troubleshooting/Firmware-Upgrade-Issues/ta-p/465761