SAI EASY 3S RS-485 connection problem and solution.

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SAI EASY 3S RS-485 connection problem and solution.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All
Related Products
product field
Schneider Electric
Square D Easy UPS 3S

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
afecomt
Crewman afecomt
Crewman

Posted: ‎2024-09-20 03:13 AM . Last Modified: ‎2024-09-20 03:14 AM

0 Likes
3
594
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-20 03:13 AM . Last Modified: ‎2024-09-20 03:14 AM

SAI EASY 3S RS-485 connection problem and solution.

Dear all 

 

we are facing multiple issues with this UPS in modbus networks. Our clients install this UPS and we do a internet-remote PLC integration through rs-485.

 

Our problem is the following

  • UPS 3S and other RS-485 devices like Schneider SLASXCV2 ---> UPS does not communicate ;SLASXCV2 does communicate.
  • UPS 3S alone ---> communicates
  • SLASXCV2 alone communicates.

How we solve?

  • Sometimes with firmware update
  • Sometimes with an RS-485 isolator
  • Change the bus (the plc has other buses)

It happened 20 times in last 2 years. 

We only offer remote plc programming support, so we are not able to perform advanced measures in field (osciloscope, multimeter, advanced conversor)

What can be the reason of this issue?

 

Thanks in advance

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
MorneMeintjes
Ensign MorneMeintjes
Ensign

Posted: ‎2024-09-25 11:42 PM

1 Like
0
485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-25 11:42 PM

Good morning.

On the screen is an option to use RS485 or Tuner. Tuner is SE's software to set up the unit. If the unit is selected for tuner RS485 will not work.

if I remember the option is under the key icon.

hope this helps.

Reply

Link copied. Please paste this link to share this article on your social media post.

afecomt
Crewman afecomt
Crewman

Posted: ‎2024-09-27 03:13 AM

0 Likes
0
460
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-27 03:13 AM

yes,

Today other issue like this.

Schenider support send us Tuner program and a procedure in order to download logs from UPS.

We will enforce field technicians to download the logs

 

Reply

Link copied. Please paste this link to share this article on your social media post.

afecomt
Crewman afecomt
Crewman

Posted: ‎2024-11-13 07:41 AM

0 Likes
0
341
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-13 07:41 AM

Nightmare continues. Now Tuner software sent by schneider did not work properly and shut downs  in the laptop of the technicians.
This UPS is still being problematic with other devices in the bus. so we always waste a whole bus of the PLC only for him. or an isolator.

 

Waiting for schneider support

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of