expansion advice

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • expansion advice
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:30 AM . Last Modified: ‎2024-03-08 12:00 AM

0 Likes
11
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:30 AM . Last Modified: ‎2024-03-08 12:00 AM

expansion advice

My current situation is, I have (2), 3 year old SU1500's. Both are at their limit, and 1 also has a replace battery notification just showing up on it. I need to add a few more servers that would probably require less than 1000 Watts.
I think I have 2 options
1) add another SU1500 and get battery replacements for the existing (2) 1500's, giving me (3) ups's
2) return the existing 2 and replace with (1) SU5000.

Option 1 seems like the most economical by 1000's of dollars.
If anyone has any suggestions for which option would be better, taking into consideration, management of the UPS's, software, managing devices on the UPS's etc. please let me know.

Thanks.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

Absolutely correct. You would be able to auto-detect the UPS when installing agents on servers 1, 5 and 9, as they would be using the Smart-Signaling port. The remaining servers would be installed as "Interface Expander - Basic" and the appropriate comm. port. PowerChute Business Edition Deluxe is available here:

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9411

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:30 AM . Last Modified: ‎2024-03-08 12:00 AM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:30 AM . Last Modified: ‎2024-03-08 12:00 AM

Thanks for the info.
Would I be able to manage 12 or so servers with 1 network card and the appropriate software or would I need 3.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:30 AM . Last Modified: ‎2024-03-08 12:00 AM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:30 AM . Last Modified: ‎2024-03-08 12:00 AM

Ron,

I'm assuming those 12 servers are going to be split amongst the 3 UPS's therefore you'll want 1 management card PER UPS so that PowerChute Network Shutdown, installed on a server, points to the IP of the NMC which is in the ups that is providing power to it.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:30 AM . Last Modified: ‎2024-03-08 12:00 AM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:30 AM . Last Modified: ‎2024-03-08 12:00 AM

Thanks for all of your insight Notorious K. You've been a really big help.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:30 AM . Last Modified: ‎2024-03-08 12:00 AM

0 Likes
0
1085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:30 AM . Last Modified: ‎2024-03-08 12:00 AM

Thanks for all of the info Notorious K. M. P.

After I thought this through for a second and realized that even though the servers and UPS's are in the same rack, they are connected to switches 50 meters away. If I was to use the NMC, I would also need to put in a UPS for the switches in the closet, and the fiber converters. The switches wouldn't be bad, but the fiber converters all have power converters the size of shoeboxes, so I would have to use power bars etc.

I think I may be looking at UPS Interface Expander Cards - AP9207 now instead.

Would I be able to implement a solution of 1 instance of PowerChute software on 1 Server to manage 3 UPS's, with connected Expander cards?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-08 12:00 AM

0 Likes
0
1085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-08 12:00 AM

Ron,

Unfortunately, the PowerChute Software doesn't work that way. The Agent portion of the software will only monitor the first UPS it detects. The other two won't be manageable. What the interface expanders are for is a Many server connection to one UPS. Not a Many UPS to One server connection.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-08 12:00 AM

0 Likes
0
1085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-08 12:00 AM

So with my scenario, to manage the shutdown procedures I would need to....

- Get the (1) 5000 unit

- Install PCBE onto 3 seperate servers to manage the 3 UPS's and also use an Interface expander on all 3 UPS's to manage multiple servers/UPS.

- Install NM software on 1 server, install a NMC into each of the 3 servers, and install UPS's along the data path between UPS -> server for any switches, fiber converters etc.

Any other solutions I may not be thinking of?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-08 12:00 AM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-08 12:00 AM

Ron,

I hope I haven't confused you or improperly relayed information. PowerChute Business Edition and the Network Management Card can't be used together. PCBE uses Serial or USB connection (on the new SUA's). PowerChute Network Shutdown is used in unison with the Network Management Card. And you would need to install PCNS onto each of the servers that need to be gracefully shutdown, the same way you would install a PowerChute Business Edition Agent onto each machine that would be connected to an expansion port.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-08 12:00 AM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-08 12:00 AM

No, I think I understand.
My question is though, from a device management perspective.

If I use PCBE on the 3 UPS scenario, I need to install the software on 3 seperate servers connected to 3 seperate UPS's. Therefore I need to log in and manage the situation at 3 different places. I'm not talking the agents on the servers, I'm talking the actual PCBE software.

If I use a NCM solution I would be able to manage it from one place.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-08 12:00 AM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-08 12:00 AM

Ron,

Actually you could do centralized mangement from one server. The server portion of PCBE will allow you to monitor up to 5 PCBE Agents, so long as they're on the same subnet. The other way to view each Agent's interface is through a web brower:

http://:3052

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
1087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

Absolutely correct. You would be able to auto-detect the UPS when installing agents on servers 1, 5 and 9, as they would be using the Smart-Signaling port. The remaining servers would be installed as "Interface Expander - Basic" and the appropriate comm. port. PowerChute Business Edition Deluxe is available here:

http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP9411

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
1086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

My current situation is, I have (2), 3 year old SU1500's. Both are at their limit, and 1 also has a replace battery notification just showing up on it. I need to add a few more servers that would probably require less than 1000 Watts.
I think I have 2 options
1) add another SU1500 and get battery replacements for the existing (2) 1500's, giving me (3) ups's
2) return the existing 2 and replace with (1) SU5000.

Option 1 seems like the most economical by 1000's of dollars.
If anyone has any suggestions for which option would be better, taking into consideration, management of the UPS's, software, managing devices on the UPS's etc. please let me know.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of