Firmware Updates - what do I need and How Do I Install it?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Firmware Updates - what do I need and How Do I Install it?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
7
3576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

Firmware Updates - what do I need and How Do I Install it?

We have a SMART UPS-1500 with Firmware Revision: 601.3.D.

The NMC IS:
Model Number: AP9617
Hardware Revision: A10

Application module information
Name: sumx
Version: v2.1.0

APC OS(AOS) information
Name: aos
Version: v2.1.1

As you can see, we are behind on Firmware version. I downloaded apc_hw02_aos355_smx355. How do I istall this onto the unit and will it cause the unit to shutdown?

Also, do I need to upgrade the SMART UPS-1500 firmware???

Thanks - Sean

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
3575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

Hello,

For starters, you cannot upgrade the EEPROM firmware on the UPS itself, that is not flash-upgradeable. But for the firmware that you downloaded, it will affect the card only. When you run the executable it will ask you to input the Network Card IP address. Do so, and then enter the Username/Password parameters. Then continue with the upgrade. It will notify you when it is complete and for the duration of the time you are doing the upgrade, you will not be able to communicate with the card other than ping.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
3576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

Hello,

For starters, you cannot upgrade the EEPROM firmware on the UPS itself, that is not flash-upgradeable. But for the firmware that you downloaded, it will affect the card only. When you run the executable it will ask you to input the Network Card IP address. Do so, and then enter the Username/Password parameters. Then continue with the upgrade. It will notify you when it is complete and for the duration of the time you are doing the upgrade, you will not be able to communicate with the card other than ping.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
3575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

I couldn't tell you either way. All I've been told is that when customers ask, it is not upgradeable, the EEPROM chip would have to be replaced. Therefore I'm suspecting it something APC Engineering takes control of

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
3575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

We have a SMART UPS-1500 with Firmware Revision: 601.3.D.

The NMC IS:
Model Number: AP9617
Hardware Revision: A10

Application module information
Name: sumx
Version: v2.1.0

APC OS(AOS) information
Name: aos
Version: v2.1.1

As you can see, we are behind on Firmware version. I downloaded apc_hw02_aos355_smx355. How do I istall this onto the unit and will it cause the unit to shutdown?

Also, do I need to upgrade the SMART UPS-1500 firmware???

Thanks - Sean

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
3575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

Hi all. Apologies for bringing this thread back from the dead, but I've got an old but very little-used Smart UPS 1500 (SUA1500I) which I recently recovered and it doesn't seem to me that the original question has been answered clearly enough (to me, at least).

After long searches, I've come to the conclusion that installing the latest firmware (PowerNet MIB v4.1.6) isn't very straightforward as the official update wizard doesn't support my model. I ran into a few posts of people who managed to do it via the serial port, but sadly they never got into specifics or linked to unavailable webpages.

So far I've downloaded a MIB file which I would need to install in some way. Do I absolutely need a network management card? I've seen that the AP9617 is still available - would it be enough to do the trick?

Please feel free to mention any thread/webpage where the procedure is thoroughly discussed - I've been searching a lot to no avail. Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
3575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

Hi,

SUA1500I is not firmware upgradable the user as it is an older UPS generation that did not support field firmware upgrades by users. Newer generation UPS models like those that start with model prefix SMT, SMC, SRT, SMX  (or in summary, those that have an LCD display on the front) support firmware upgrades to them and it can be done via a Network Management Card 2 (AP9630/31) and Firmware Upgrade Wizard using a file we provide for those UPS models only.

Adding a UPS network management card for your UPS won't help you upgrade the UPS since upgrading the UPS isn't option to begin. 

The PowerNet MIB is only used for users who use a Network Management Card and SNMP for network management/monitoring of the UPS. If users use a Network Management Card, like AP9617 you mentioned, it (AP9617) supports firmware upgrade on it but that would be it.

Hope that helps clarify.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
3575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

Thanks for your reply, Angela. I was misled by a page on the APC website that lists the SUA1500I firmware as upgradeable - here it is:

http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=SUA1500I&xtmc=sua1500i&xtcr...

And as the firmware was quite recent, I was eager to try to install it. Cheers!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

0 Likes
0
3575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 06:31 AM . Last Modified: ‎2024-03-07 11:59 PM

Ohh, I see. Yes, I don't think that should be listed since an SNMP MIB cannot be loaded on to a UPS. Sorry for the confusion you were put through!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore