DLA1500 Vs. SUA1500

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • DLA1500 Vs. SUA1500
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:29 AM . Last Modified: β€Ž2024-03-08 12:01 AM

0 Likes
13
3447
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:29 AM . Last Modified: β€Ž2024-03-08 12:01 AM

DLA1500 Vs. SUA1500

I found myself in the market for a smart-ups, and i purchased one last night from a vendor in Florida

I was under the FULL impression it was a SUA1500 however as ive looked at the shipping invoice online i see that its a DLA1500

Should i be concerned? what are the differences between these units?

Message was edited by: klehmann

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

0 Likes
0
3440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

I found myself in the market for a smart-ups, and i purchased one last night from a vendor in Florida

I was under the FULL impression it was a SUA1500 however as ive looked at the shipping invoice online i see that its a DLA1500

Should i be concerned? what are the differences between these units?

Message was edited by: klehmann

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 13
Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:01 AM

0 Likes
0
3440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:01 AM

do you know how the sensitivity is set on this unit? i understand on the SUA1500 it is selectable to LOW MED and HIGH. I would like this unit to run on high sensitivity for maximum protection, the fact that this feature is disabled leaves me to think they are somewhat different? Unfortunately, the vendor was not dell, so if this unit fails i do not think i will be covered by APC or Dell support.

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:01 AM

0 Likes
0
3440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:01 AM

Sorry that I wasn't clear enough with the differences. The UPS just doesn't have external adjustable sensitivity. You can still install PowerChute Business Edition and adjust the sensitivity. By defautl, the Dell UPS's are set to High.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:01 AM

0 Likes
0
3440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:01 AM

Thank you so much for your quick well informed responses...

I was ready to go into panic mode here. Any reason to be alarmed? They will provide the exact same features and perform to the exact same specifications?

Reply

Link copied. Please paste this link to share this article on your social media post.

TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
Sisko

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:01 AM

0 Likes
0
3440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:01 AM

Absolutely no need to worry. They are physically the same UPS and will operate to the exact same specifications, and outside of the DLA not having external adjustable sensitivity control, they are the exact same UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:01 AM

0 Likes
0
3440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:01 AM

Hi
Follow up question.
Knowing that Powerchute does not jive with Apple Imacs. I probably wont be able to adjust the sensitivity on a DLA1500 vs the SUA1500 units as you can only do this through Powerchute. Is there any reason that I would want to lower the sensitivity of this unit using it with my Imac.
Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

0 Likes
0
3440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

Hi John,

Our UPS checks if there's an acceptable voltage and frequency on the outlet where it is connected. If it detects a sudden shift and or change it will transfer to On Battery mode. If you have an unreliable power source, frequency keeps on shifting and or on generator power we advise our customers to change the sensitivity to widen the acceptable threshold of the UPS.

- JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

0 Likes
0
3440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

Double Post. Sorry

Message was edited by: JonPro

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

0 Likes
0
3440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

Hi
Thanks for the reply.

When you say our UPS, do you mean both the SUA and DLA?

And when you say, "You advise customers to change sensitivity to widen the acceptable threshold of the UPS," are you implying that one should use the HIGH sensitivity default setting, regardless?

Again thanks so much for replying to my questions

John

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

0 Likes
0
3440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

John,

What Buzz had said above was right. The settings and or behaviors applies to both SUAs and DLAs. There shouldn't be no problem leaving the setting to High as long as the UPS doesn't produce and or behave differently. If it does then that is when we would adjust the settings.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

0 Likes
0
3440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

Yes, he meant both. The SUA and DLA models are essentially identical, as has been already explained.

The default setting is fine for most applications, yes.

Unless you're seeing the UPS (either the SUA or the DLA, since they are the same) going to battery excessively, you can change the sensitivity. But unless you have a generator or very dirty power, you shouldn't need to worry about it, and even then you could always borrow another computer just long enough to install the software, change the setting, and then remove the software. The setting will remain after you change it, even without the software there for monitoring.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

0 Likes
0
3440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

Thanks for the info guys. Clears up alot of queries I have. Just waiting for my Imac to arrive. Buzz, I do realize that the specs are the same, and know this was explained previous, but my question was regarding the only difference between the the two units. And when I asked, if he was talking about the SUA and/or DLA as being their unit, being that the DLA is manufactured for Dell by APC, just wanted to know that I was on the same page as JonPro we he mentioned "OUR UPS" and not separating between Dell and APC.
Who knows, this may clear it up for others who may have the same questions.
Thanks again

Message was edited by: bakes99

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

0 Likes
0
3440
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

Yep, no problem. I can see how "our" might exclude the Dell model. πŸ™‚

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

0 Likes
0
3441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2021-06-30 06:30 AM . Last Modified: β€Ž2024-03-08 12:00 AM

I found myself in the market for a smart-ups, and i purchased one last night from a vendor in Florida

I was under the FULL impression it was a SUA1500 however as ive looked at the shipping invoice online i see that its a DLA1500

Should i be concerned? what are the differences between these units?

Message was edited by: klehmann

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Β 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore