Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
detect ups over network only ?
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3005:10 AM. Last Modified: 2024-03-0803:08 AM
detect ups over network only ?
Hi there,
I have a apc smart ups 5000 equipped with network management card.
this card is configured and working.
However, if i want to install an agent, it is obviously required to connect the
ups with serial or usb cable to the computer to detect it.
As my computers are blade systems, this is impossible, and installation of
an agent is therefore unable to detect the ups.
Question is, how can i install an agent, if the only connection is over
tcp/ip network ?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3005:10 AM. Last Modified: 2024-03-0803:08 AM
Hello,
You are correct in that PowerChute Business Edition will only work over Serial or USB. For software integration with Network Management Cards, APC has PowerChute Network Shutdown. PCNS as it's called, will need to be installed on each client in place of the PCBE Agent. It will verify communication with the UPS's Network Management Card during startup, and add itself to the PowerChute Client list in the NMC. Please keep in mind that the network needs to remain up and running during a power loss in order for this to work efficiently.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-3005:10 AM. Last Modified: 2024-03-0803:08 AM
Hello,
You are correct in that PowerChute Business Edition will only work over Serial or USB. For software integration with Network Management Cards, APC has PowerChute Network Shutdown. PCNS as it's called, will need to be installed on each client in place of the PCBE Agent. It will verify communication with the UPS's Network Management Card during startup, and add itself to the PowerChute Client list in the NMC. Please keep in mind that the network needs to remain up and running during a power loss in order for this to work efficiently.