Symmetra LX 16000 - Restore output power after UPS shuts down

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra LX 16000 - Restore output power after UPS shuts down
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
121
Erasmus_apc
Sisko Erasmus_apc
112
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

0 Likes
7
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

Symmetra LX 16000 - Restore output power after UPS shuts down

I talked to APC tech support on this issue. After a prolonged power outage and the UPS shuts itself off when the power is restored shouldn't it also turn itself back on and restore output power to the connected devices? I really do not want to have to manually push a couple buttons to restore power to all of our servers and network equipment (especially in the middle of the night). I know you can turn the UPS on via the network interface; doesn't help much when the router/firewall is not powered on though... Tech support says there is no way to automate turning on output power after the UPS is turned off. Is this true?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

yeah.

sounds like that event happened and then unfortunately, the power came back on but the server was already starting to shutdown and couldnt stop.

maybe you can just have it configured to shutdown based on "UPS: on battery" instead of "Runtime exceeded" in addition.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

the UPS should boot back online. i tested this myself after hearing different answers about this. I tested it with a Symmetra LX myself.

as long as you have the setting in the network management card set to "Restart when power is restored" it should power back up (this setting is located, in the newest firmware, under the UPS tab->Powerchute configuration). any servers that you want to power back on need to be set correctly in the BIOS to "last state" or "always on" or something along those lines.

say the power goes out, the servers shut down but before the UPS turns off, the power returns, the UPS will NOT have rebooted so thus the servers will not turn back on (they have seen either utility power or battery power during the entire outage so that is why the UPS needs to reboot for them to turn back on). to get around this issue, you can set the last server to shutdown to turn off the UPS as well so that when the power comes back on, the UPS will have been shutdown and thus power back up.

hope this helps! let me know if you have any other questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

That is what always happened in the past. Never had a problem. This is the second time this has happened though. Here is the log:

10/13/2008 01:22:14 Environment: Restored the local network management interface-to-integrated Environmental Monitor Input T Sensor (Integrated at Int Sensor Loc) communication.
10/13/2008 01:21:16 UPS: The output power is turned off.
10/13/2008 01:21:16 UPS: Restored the local network management interface-to-UPS communication.
10/13/2008 01:20:47 System: Network service started. System IP is 172.16.2.93 from manually configured settings.
10/13/2008 01:20:47 System: Warmstart.
10/13/2008 01:09:03 UPS: The output power is turned off.
10/13/2008 01:04:25 UPS: A graceful shutdown process is being used to shut down the load equipment before the UPS turns off. Initiated by PowerChute ns from 172.16.2.41.
10/13/2008 00:59:43 UPS: No longer on battery power.
10/13/2008 00:58:57 UPS: On battery power in response to an input power problem.

Seems kind of odd that the UPS was only on battery power for a minute and 5 min later shuts everything down. My main concern right now though is "The output power is turned off." When input power is restored the output power remains off. I have to manually turn it back on through the control panel or web interface.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

can you tell me what configuration you have on the powerchute client at IP address 172.16.2.41? is it set to shutdown on a particular event (such as UPS: on battery)? this is located at http://172.16.2.41:3052 under the server name->configure events. there will be a check mark in the shutdown column if any special settings are configured.

also, please tell me how much runtime you have on the UPS and confirm what the low battery duration is set to inside of the network management card.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

Yes, I want to shut down the system. checked
Shutdown the system only when the event lasts this long (seconds): 600

Runtime is 19min
Low battery duration is set to 2min

Thanks for your quick response!

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

are there any other events configured to shutdown? the power outage was only very brief yet this server sent a shutdown command even though that event didnt last 600 seconds.

can you post the event log from the powerchute network shutdown interface on this server?

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

Runtime: Exceeded: 300 sec

guessing this is what caused it.

10/13/2008 01:51:10 Shutdown process started. Windows 2003 will shut down soon.
10/13/2008 01:51:10 Available runtime is sufficient.
10/13/2008 01:46:30 Input power has been restored: UPS has switched to On Line operation
10/13/2008 01:46:10 Available runtime has been exceeded.
10/13/2008 01:45:43 UPS has switched to battery power

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

0 Likes
0
1681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:08 AM

yeah.

sounds like that event happened and then unfortunately, the power came back on but the server was already starting to shutdown and couldnt stop.

maybe you can just have it configured to shutdown based on "UPS: on battery" instead of "Runtime exceeded" in addition.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of