Posted: 2021-06-30 05:10 AM . Last Modified: 2024-03-08 03:08 AM
I have an APC UPS Smart-1000 which was connected via a USB cable with an HP Proliant 350 server with Windows 2003 server, using the PowerChute Business Edition ver. 7.0. Everything was fine for almost 2 years now until we had to send it for replacement of the batteries. The local engineer also told me that they do a reset of the cpu regarding the batteries.
The problem now is that although nothing have changed on the server, the PowerChute does not detect the ups. I have removed and reinstall the PowerChute with no luck. Also when I try manually to detect the ups I am only prompted to select the network range while the ups is connected via USB.
On the reinstallation of the PowerChute agent I saw that it was detected but then no device was appeared in the Powerchute server or Console.
Any idea?
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:10 AM . Last Modified: 2024-03-08 03:08 AM
For starters, you should try a Brain-Dead of the UPS:
1. Turn off the load
2. Turn off the UPS and unplug the load
3. Disconnect the UPS from the wall
4. Depress the Off button for 4-6 seconds until you hear a click
5. Reconnect everything and reinstall PCBE.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 05:10 AM . Last Modified: 2024-03-08 03:08 AM
For starters, you should try a Brain-Dead of the UPS:
1. Turn off the load
2. Turn off the UPS and unplug the load
3. Disconnect the UPS from the wall
4. Depress the Off button for 4-6 seconds until you hear a click
5. Reconnect everything and reinstall PCBE.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.