Symmetra doesn't see battery modules

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra doesn't see battery modules
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:07 AM

0 Likes
5
2392
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:07 AM

Symmetra doesn't see battery modules

I have a Symmetra 12k I picked up via auction. It fires up nicely and doesn't seem to have any problems except that it refuses to acknowledge any batteries are installed.

I've replaced the 4 that were installed in the main unit with the 4 that were in the XR cabinet with no change. Status says 0 modules 0 bad. I have set the options to default values with no change.

IIRC, the power module(s) have to be on (fan spinning) in order to charge the batteries. None of them are on. They all pass diagnostics and the system also recognizes if any are removed or added.

Any ideas?

Bill

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • symmetra
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:11 AM . Last Modified: ‎2024-03-08 03:07 AM

0 Likes
0
2390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:11 AM . Last Modified: ‎2024-03-08 03:07 AM

good to hear bill. thanks for the update.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:07 AM

0 Likes
0
2390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:07 AM

As suggested, a known good and charged battery got everything going.

Bill

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:07 AM

0 Likes
0
2390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:07 AM

i am assuming that you have no load on this UPS? if so, you can proceed.

i'd first start by doing a "frame sweep." I would suggest starting by putting the UPS into maintenance bypass and removing all modules. You want to find the system enable switch on the back and turn the UPS off, then back on. just start with putting the main intelligence module on the UPS and seeing what you get. you should get error messages such as "no power modules" and "batteries discharged" since there are none. then proceed with placing the redundant intelligence module in the system and then toggling the system enable switch again. make sure all the error messages make sense again, such as batteries discharged, etc. proceed by then adding a power module and then toggling the system enable switch on the back again. turn it back on and make sure you have no faults besides about bypass and then batteries discharged. if everything looks good, add one battery again and turn the system off via system enable again and then turn it back on and see if theres any change with the battery count. if there IS, proceed with a power module then battery combo until you see any weird changes.

essentially, you want to add each module, one by one while resetting the system via the system enable switch in between each module. if you do this and you still see 0 batteries, i'd have to lean towards a problem with the main intelligence module or something that damaged all of the battery bays for some reason.

if you don't feel comfortable performing any of these actions, please call into tech support at 800-890-4272 or of course you can post any additional questions here if you'd like before starting.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:07 AM

0 Likes
0
2390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:10 AM . Last Modified: ‎2024-03-08 03:07 AM

Tech support is writing it off as likely a problem with the SYBATT's being fully discharged and of unknown condition.

I'll be buying a new module and see if that will allow it to go online.

Bill

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:11 AM . Last Modified: ‎2024-03-08 03:07 AM

0 Likes
0
2390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:11 AM . Last Modified: ‎2024-03-08 03:07 AM

i apologize! i thought you said you replaced 4 modules by buying them but i re-read it and you said you moved them from the XR to the main frame.

if the batteries are below about 100 volts or so, they may not be recognized.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 05:11 AM . Last Modified: ‎2024-03-08 03:07 AM

0 Likes
0
2391
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 05:11 AM . Last Modified: ‎2024-03-08 03:07 AM

good to hear bill. thanks for the update.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore