Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

correct battery count setting??

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • correct battery count setting??
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

0 Likes
4
852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

correct battery count setting??

i've been searching through lots of documentation and can't find a solid answer to this,


what battery count should i put in powerchute for my ups?,

i've got a SU3000RMXLI3U with one SU48RMXLBP3U,
with a the total PBC27 battery pack count of three.

i've got this set to 2 at the moment, as i've seen "discount the ups internal pack", is this correct??

thanks

Matt

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • battery
  • PowerChute
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

0 Likes
0
852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

Thanks for the quick reply,
If its there in the manual, I didn't see it!!

i've set it to 1 pack now, but i'm still curious....



an exerpt from Knowledge Base #63

*Note: A SU48RMXLBP is a large capacity battery. It is equivalent to
two standard external batteries; therefore, for each SU48RMXLBP input 2 (two)
batteries.

so this does not apply in my case??

Thanks

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

0 Likes
0
852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

i've been searching through lots of documentation and can't find a solid answer to this,


what battery count should i put in powerchute for my ups?,

i've got a SU3000RMXLI3U with one SU48RMXLBP3U,
with a the total PBC27 battery pack count of three.

i've got this set to 2 at the moment, as i've seen "discount the ups internal pack", is this correct??

thanks

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

0 Likes
0
852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

If needed, you can adjust the battery count easily with a basic terminal emulator.  (Such as HyperTerm or PuTTY in windoze)

Here's how:

  1. Hook up a computer to the UPS via a APC "smart" serial cable. If you don't have a serial port on your computer, you can use a USB to serial converter.  You must use an APC cable, as the UPS uses a non-standard pinout.
  2. Start up a terminal emulator such as HyperTerm or PuTTY (with serial support).
    Port settings are: 2400 baud, 8 data bits, 1 stop bit, no parity, flow control is Xon/Xoff. When using HyperTerm, make sure FIFO buffer is NOT set.
  3. When connected, you will NOT be greeted by any prompt!  Typing in Shift + Y should show the letters SM in the terminal window, this will confirm your connection.
  4. Press > to see the current battery pack count. If no battery packs were installed, it should say 0.
    Pressing + will add one pack to the count, - will subtract the count by one. If you have multiple packs, press + several times to add them all. When finished, press > again to check the count.
  5. When finished, you can simply close the window (or end the connection in HyperTerm).

-Phil

Reply

Link copied. Please paste this link to share this article on your social media post.

Erasmus_apc
Sisko Erasmus_apc
Sisko

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

0 Likes
0
852
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

It should be set for "1". You discount the internal pack, yes, but you count an external battery pack as one. You do not count per RBC27 module, just per battery pack. The manual for the battery pack (quickly) covers this in one of the examples provided.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

0 Likes
0
853
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

Thanks for the quick reply,
If its there in the manual, I didn't see it!!

i've set it to 1 pack now, but i'm still curious....



an exerpt from Knowledge Base #63

*Note: A SU48RMXLBP is a large capacity battery. It is equivalent to
two standard external batteries; therefore, for each SU48RMXLBP input 2 (two)
batteries.

so this does not apply in my case??

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of