Symmetra PX MIB fle required along with defined OID

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Symmetra PX MIB fle required along with defined OID
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:36 PM . Last Modified: ‎2024-03-14 04:18 AM

0 Likes
10
3478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:36 PM . Last Modified: ‎2024-03-14 04:18 AM

Symmetra PX MIB fle required along with defined OID

Good Day,

I am working on a Symmetra PX UPS.

The UPS is connected with 06 Nos. of Power Modules and it is also connected with 12 Nos. of PDM's

I wish to read all the values of UPS, Power Module and PDM via SNMP, I have a MIB file but when i use SNMP WALK i just get OID (1.3.5.6.7.8.9.) and value i am not getting any object name in SNMP Walk.

It would be great help if someone share a file which defines OID along with Object names.

Thank You.

Genjua

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • mib
  • oid
  • snmp
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

0 Likes
0
3474
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

Can you confirm which version of the MIB you've loaded? You should have at least 4.1.X - which I think the latest is 4.1.2. See my screenshot using 4.1.2. My guess is the MIB you have is possibly outdated.

nXYLqFmL%2Fl8dr6qkEvDRPg%3D%3D.jpegnXYLqFmL%2Fl8dr6qkEvDRPg%3D%3D.jpeg

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:36 PM . Last Modified: ‎2024-03-14 04:17 AM

0 Likes
0
3473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:36 PM . Last Modified: ‎2024-03-14 04:17 AM

any help?

i just need names along with their OID for symmetra PX connected with 06 Nos. of Power Modules and it is also connected with 12 Nos. of PDM's.

I hope you guys understand my question, if not let me know?

Genjua

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:36 PM . Last Modified: ‎2024-03-14 04:17 AM

0 Likes
0
3473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:36 PM . Last Modified: ‎2024-03-14 04:17 AM

Hi,

What MIB file do you have? You'll want ot make sure you loaded/compiled the APC PowerNet MIB from http://www.apc.com/tools/download/index.cfm 

You'll maybe want to look into how the SNMPwalk tool works. I worked with some one recently that used SNMPwalk and the tool was not walking APC specific OIDs if he walked it from the top. All APC specific OIDs will be here and beyond: .1.3.6.1.4.1.318 .. you might try walking specifically from there, using the proper syntax. Most of the OIDs for this UPS (or any) will be under .iso.org.dod.internet.private.enterprises.apc.products.hardware.ups or .1.3.6.1.4.1.318.1.1.1. It also may be helpful to try a graphical MIB browser like GetIf or iReasoning to browse so you know which OIDs may be of interest to you versus using a CLI tool like SNMPwalk.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:36 PM . Last Modified: ‎2024-03-14 04:17 AM

0 Likes
0
3474
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:36 PM . Last Modified: ‎2024-03-14 04:17 AM

Angela, I am glad to hear that the pain which i am facing you have already faced 🙂

Well i am using IReasoning MIB Browser and using WALK against the APC MIB file for UPS Symmetra IP.

after that i am able to view UPS and its batteries OID's and i have chosen OID of my choice, Now like i mentioned in my first post that UPS is connected along with Power Modules and PDM's i wish to monitor PDM Breaker Status, Its Current Its volatge using same MIB file but i am unable to view that.

I am looking for some file which defines product OID along with its name so that i pick up the OID which i want to use and leave the rest.

Genjua

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:36 PM . Last Modified: ‎2024-03-14 04:17 AM

0 Likes
0
3474
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:36 PM . Last Modified: ‎2024-03-14 04:17 AM

Hi - the only MIB file we have is the giant MIB file that contains all of the OIDs for APC products. Most people usually walk it to see what is available and then have your monitoring program (that is not necessarily a MIB browser) only poll the ones that you're interested in.

Are you going to be strictly using iReasoning or were you just using that to browse before you load OIDs into a different system for long term monitoring? This is a UPS so it will give you a lot of OIDs from .iso.org.dod.internet.private.enterprises.apc.products.hardware.ups but you could also start from .iso.org.dod.internet.private.enterprises.apc.products to make sure that you get all possible OIDs relating to the power distribution. I don't have one of these systems to check on but I imagine some of the modular PDU stuff you're looking for is under .iso.org.dod.internet.private.enterprises.apc.products.hardware.isxModularDistribution or .iso.org.dod.internet.private.enterprises.apc.products.hardware.isxModularPdu so I'd try walking those if you can and see what you get.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:36 PM . Last Modified: ‎2024-03-14 04:17 AM

0 Likes
0
3474
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:36 PM . Last Modified: ‎2024-03-14 04:17 AM

I am using iReasoning just for initial WALK after that i will chose my desire OID and monitor it over front end software.

Is there is any other browser that you will advise to use for MIB WALK?

I will check isxModularDistribution or .iso.org.dod.internet.private.enterprises.apc.products.hardware.isxModularPdu and will update you.

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:36 PM . Last Modified: ‎2024-03-14 04:17 AM

0 Likes
0
3474
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:36 PM . Last Modified: ‎2024-03-14 04:17 AM

Please check the attached sheet screen shot, I am unable to found isxModularDistribution OR isxModularPdu

Angela, any advise at this stage will be highly appreciated.

Thanks once again.

Genjua

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

0 Likes
0
3475
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

Can you confirm which version of the MIB you've loaded? You should have at least 4.1.X - which I think the latest is 4.1.2. See my screenshot using 4.1.2. My guess is the MIB you have is possibly outdated.

nXYLqFmL%2Fl8dr6qkEvDRPg%3D%3D.jpegnXYLqFmL%2Fl8dr6qkEvDRPg%3D%3D.jpeg

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

0 Likes
0
3474
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

Angela, its powernet412

Please upload the MIB file which you have.

Thanks.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

0 Likes
0
3474
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

Angela You are right, Thanks for your support i was using OLD version and due to that i was unable to view ISXModular.

Basically i have 2-3 files, the one which i ws using is 318 version, Now i have loaded 4.1.2 which show ISXModular folder in the MIB Browser.

Thanks Much once again.

Genjua

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

0 Likes
0
3474
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:37 PM . Last Modified: ‎2024-03-14 04:16 AM

No problem - you're welcome.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of