connecting and monitoring multiple UPS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • connecting and monitoring multiple UPS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
145
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

0 Likes
6
1175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

connecting and monitoring multiple UPS

Can you hook up multiple rack mounted UPS up to a stand alone computer to monitor all the UPS's on the stand alone computer?

for instance say I have 4 APC UPS's hooked up with multiple peices of equipment hooked into them for power. But I can not add power chute to the equipment to monitor the events and batteries. is hooking all 4 UPS's to a stand alone CPU to monitor the UPS's a viable option so I can see the power events and monitor the batteries?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

0 Likes
0
1175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

No, unfortunately the software only supports one instance on each computer so it'd only be able to actively monitor one UPS via USB or serial. Same also applies for doing graceful shutdown via the software via USB or serial.

I'd suggest getting a UPS Network Management Card for the UPS and you can then monitor those via the network inside each UPS via IP address. If interested, your options would be AP9630 or AP9631 for the current offering of management cards. Depending on UPS model, some of our older management card models may work too if you have some available or would rather purchased used. (Those would be AP9617, AP9618 or AP9619 or even AP9606 for the basics). But again, not every UPS supports every type of management card so I'd have to help you verify UPS models to make a suggestion.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

0 Likes
0
1175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

Can you hook up multiple rack mounted UPS up to a stand alone computer to monitor all the UPS's on the stand alone computer?

for instance say I have 4 APC UPS's hooked up with multiple peices of equipment hooked into them for power. But I can not add power chute to the equipment to monitor the events and batteries. is hooking all 4 UPS's to a stand alone CPU to monitor the UPS's a viable option so I can see the power events and monitor the batteries?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

0 Likes
0
1176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

No, unfortunately the software only supports one instance on each computer so it'd only be able to actively monitor one UPS via USB or serial. Same also applies for doing graceful shutdown via the software via USB or serial.

I'd suggest getting a UPS Network Management Card for the UPS and you can then monitor those via the network inside each UPS via IP address. If interested, your options would be AP9630 or AP9631 for the current offering of management cards. Depending on UPS model, some of our older management card models may work too if you have some available or would rather purchased used. (Those would be AP9617, AP9618 or AP9619 or even AP9606 for the basics). But again, not every UPS supports every type of management card so I'd have to help you verify UPS models to make a suggestion.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

0 Likes
0
1175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

great that helps me a lot. now i can figure out where i need to go from here. i will get the model numbers of the UPS's and add them to the thread and maybe you can help me out with the correct configuraation.

Thasnks once agian.

John

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

0 Likes
0
1175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

Sounds good to me!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

0 Likes
0
1175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:28 PM

the model number for the UPs is BR1500 8 ea in this one room. i have serial numbers if that will help. Let me know. thanks for the help.

John

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:27 PM

0 Likes
0
1175
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:30 AM . Last Modified: ‎2024-03-12 11:27 PM

Ok, this is a Back UPS product unfortunately so what I mentioned does not apply. Network Management Cards are only supported in Smart UPS and essentially most larger UPS models besides BR1500 and other Back UPS.

Your options would be one computer per BR1500 UPS via USB monitoring or upgrade the UPSs to Smart UPS or similar where a Network Management Card accessory is available and supported. (Back UPS do not even have a location on them physically to install accessories).

Let me know if you have any questions.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore