I'm working on connecting two SmartUPS 1000 and configuring them to notify us in the event of powerissues. Unfortunately, I cannot get email or pager notifications to go through because SMTP authentication is required to send mail within my company. Mail is hosted external and so all email traffic must authenticate to go through.
I don't believe that the hosting provider will make any changes, and since there is no way to setup authentication through the PowerChute software, I'm kind of stuck. I proposed setting up an SMTP or sendmail server , but my director doesn't want one internal to the company.
I called APC support and they recommended setting up an SNMP server and have that server authenticate through SMTP to send email. Has anyone done this and can they point me in the right direction?
I've configured SNMP on the server that I'm using as the APC Server, but I understand I also need to setup an SNMP server with the APC MIB, and I'm completely in the dark about that. Any assistance would be greatly appreciated!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:55 AM . Last Modified: 2024-03-07 10:24 PM
So you're using SNMP to have a trap from the APC device sent to some type of NMS, which is then in turn going to send the email?
SNMP from an APC device cannot authenticate any type of email, nor even send email, it's SNMP.
To me, it doesn't seem like the combination of SNMP and an SMTP server that requires authentication is going to work, unless your NMS can authenticate.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:55 AM . Last Modified: 2024-03-07 10:24 PM
At this time, the firmware does not allow for coding of authentication to send email from the Network device.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:55 AM . Last Modified: 2024-03-07 10:24 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:55 AM . Last Modified: 2024-03-07 10:24 PM
I don't know what happened, but my message got truncated. Here is the rest of it: I don't believe that the hosting provider will make any changes, and since there is no way to setup authentication through the PowerChute software, I'm kind of stuck. I proposed setting up an SMTP or sendmail server , but my director doesn't want one internal to the company. I called APC support and they recommended setting up an SNMP server and have that server authenticate through SMTP to send email. I've configured SNMP on the server that I'm using as the APC Server, but I understand I also need to setup an SNMP server with the APC MIB, and I'm completely in the dark about that. Has anyone done this and can they point me in the right direction? Any assistance would be greatly appreciated!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:55 AM . Last Modified: 2024-03-07 10:24 PM
So you're using SNMP to have a trap from the APC device sent to some type of NMS, which is then in turn going to send the email?
SNMP from an APC device cannot authenticate any type of email, nor even send email, it's SNMP.
To me, it doesn't seem like the combination of SNMP and an SMTP server that requires authentication is going to work, unless your NMS can authenticate.