Shutdown UPS Before Run Time Expires
  • Shutdown UPS Before Run Time Expires
Posted: ‎2021-06-30 07:55 AM . Last Modified: ‎2024-03-07 10:25 PM
1473
Short Story: We want the UPS to shutdown at 30 minutes (run time currently 1 hour 16 mins) to make sure space does not overheat.  We do not use PowerChute.
Symmetra 8K (Mfg date: 12/2/2009) with equipment that cannot be controlled with PowerChute.
Posted: ‎2021-06-30 07:55 AM . Last Modified: ‎2024-03-07 10:24 PM
If you upgrade the NMC to a AP9630 or AP9631 you will have the options that Matt suggested.
Hi Don
Which NMC do you have installed in the Symmetra?  The manufacture date is around the time that the 2nd Generation NMCs came out and they have the below section for on the shutdown page, which has settings that are not present on the AP9619.
Regards
Matt
Unfortunately it is the older version of UI and does not have those options.  Unless I am not seeing the logic...