battery fault of Symmetra LX 8KVA

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • battery fault of Symmetra LX 8KVA
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
114
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

0 Likes
5
3281
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

battery fault of Symmetra LX 8KVA

hi guys,

2 module was installed on the unit, UPS detected 1 battery module fault few minutes after we removed the faulty battery module the UPS detected the remaining module is faulty.
We ask the user to shutdown all the load, because were going to power off the UPS. We power off the UPS and install back all the battery module and power on again, and everything back to normal. On the next day Battery fault again, this time the other battery module got an error.

Note: The unit is out of warranty and the battery was new.

Someone advise me to get the log event from MIM and RIM but i dont how to do that..

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

0 Likes
0
3283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

As Matt said, the raw status of the MIM and RIM won't really help much. I suggest you follow the instructions initially provided to get the info needed to determine the issue. I'd also stress the fact that you shouldn't ever need to turn off the equipment or the Symmetra itself. The whole point of a UPS is to prolong uptime, not eliminate it.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

0 Likes
0
3283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

Greetings,

Why did they user have to shut down all the load? That should almost never be necessary with Symmetra, given it has its own maintenance bypass switch. With that engaged, you could toggle the System Enable switch and essentially reboot the UPS electronics, without interrupting power to customer's equipment.

When the batteries showed as bad, did you gather any of the data from the Diags menu in the PowerView? Could you please install the "bad" batteries and provide the following for review:

Go to DIAGS - > BATTS - > Status 2 of 2 - >

Now you will be at the individual battery status, such as:
Battery 1 of 4 1/5
Main Frame Module: R2
Level 2 from Top
Status: OK

Now press the enter button. You will be on page 2/5 (see top right corner). Record the data here. Then press the enter button to record the data on pages 3, 4 and 5.

Then gather data from the other suspect battery.

Also, what is the Master FW rev on the Main Intel Module and Redundant Intel Module?

This info will be very helpful in determining what is happening with those battery modules.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

0 Likes
0
3283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

Hi Matt

we ask the user to shutdown all load to protect their machine, b'coz frequent power failure occur on the site. All we got was from the MIM and RIM raw status.
can u help me to understand this code:

MIM
M 05 0000 0000 0200
0000 0000 E0F9 006B
00079DDB 0087F1AD

RIM
R 05 0000 0000 0200
0000 0000 E0F9 806B
00079DDB 0087F1AD

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

0 Likes
0
3283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

UP UP

Any one can help me to understand the code:

Thanks

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

0 Likes
0
3283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

Raw status is simply a live snapshot, so we can see that the UPS is online normally with at least one battery module fault present.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

0 Likes
0
3284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

As Matt said, the raw status of the MIM and RIM won't really help much. I suggest you follow the instructions initially provided to get the info needed to determine the issue. I'd also stress the fact that you shouldn't ever need to turn off the equipment or the Symmetra itself. The whole point of a UPS is to prolong uptime, not eliminate it.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of