Network Monitoring - Standard On The SMT750?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Network Monitoring - Standard On The SMT750?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

0 Likes
5
4226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

Network Monitoring - Standard On The SMT750?

We are looking at doing a major network upgrade this summer in preparation for a VOIP deployment next summer. That preparation consists of replacing network edge switches in all of our closets. Along with those switch replacements, I want to put in UPS units that I can hook into the network and monitor from a central server. I don't need any shutdown capabilities or real management capability from the units, as I don't know of any switches that can be powered off gracefully. I just want to be able to monitor them in terms of the state of the battery...whether it's still good or not...whether the unit is online...etc.

I have been looking at the SMT750, and it states that it "provides remote management over a network". Does it provide that remote management without an add-in smartslot card, or do you have to buy the network management card for the unit as well? Is the UPS monitoring port on the back that looks like an ethernet RJ45 really just a serial port?

Any info is greatly appreciated!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

0 Likes
0
4226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

Thank you for the answer. Out of curiosity, does APC offer any small UPS devices that do have a network interface? It would seem like a popular product for wiring closets. The SMT750 is actually overkill for what I need, since I have no closets with more than one edge switch, but it seemed like the smallest that would provide network manageability.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

0 Likes
0
4226
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

Hi, I have been looking at the SMT750I, and it states that it "provides remote management over a network". Does it provide that remote management without an add-in smartslot card, or do you have to buy the network management card for the unit as well?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

0 Likes
0
4227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

Thank you for the answer. Out of curiosity, does APC offer any small UPS devices that do have a network interface? It would seem like a popular product for wiring closets. The SMT750 is actually overkill for what I need, since I have no closets with more than one edge switch, but it seemed like the smallest that would provide network manageability.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

0 Likes
0
4225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

The [BackUPS HS|http://www.apcc.com/products/family/index.cfm?id=3] seems to fit your requirements. It doesn't use the Network Management Card technology, so be sure to flip through the manual to get an idea of the web interface's capabilities.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

0 Likes
0
4225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

The SMT750 UPS does not ship with the NMC installed. You will need to purchase the NMC separately if you want to monitor it on the network. The RJ45 which is available at the rear of the unit is for Serial communication.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

0 Likes
0
4227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

Hi, I have been looking at the SMT750I, and it states that it "provides remote management over a network". Does it provide that remote management without an add-in smartslot card, or do you have to buy the network management card for the unit as well?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

0 Likes
0
4225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 12:01 AM . Last Modified: ‎2024-03-14 01:06 AM

Hi,

You can install a network management card. Part numbers AP9630 or AP9631. Another option is to install PowerChute Business Edition on the OS (if compatible) and mange the UPS through PowerChute. PowerChute Business Edition is available for down load on apc.com

Note: If you only have 1 UPS you only need to install the PowerChute Agent. You do not need to install the PowerChute Server and Console. You will manage the UPS via the PowerChute Agent web interface. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore