apcupsd can't connect to Smart-UPS 2200/Network Management Card 2

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • apcupsd can't connect to Smart-UPS 2200/Network Management Card 2
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 02:13 AM . Last Modified: ‎2024-02-29 10:13 PM

0 Likes
1
3413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:13 AM . Last Modified: ‎2024-02-29 10:13 PM

apcupsd can't connect to Smart-UPS 2200/Network Management Card 2

Hi,

I've got a problem to reach an UPS with apcupsd over ethernet.

Here my Setup:

Smart-UPS 2200 (Firmware Revision: UPS 09.3 (ID18)) with an Network Management Card 2 - AP9630 (Version: v6.2.0)
DNS bvg-usv001
IP 192.168.65.24
debian host with apcupsd
DNS bund-shutdown
IP 192.168.66.26

The apcups_conf:

UPSNAME bvg-usv001
UPSCABLE ether
UPSTYPE pcnet
DEVICE 192.168.65.24:admin:test123

LOCKFILE /var/lock
SCRIPTDIR /etc/apcupsd
PWRFAILDIR /etc/apcupsd
NOLOGINDIR /etc
ONBATTERYDELAY 6
BATTERYLEVEL 5
MINUTES 3
TIMEOUT 0

ANNOY 300
ANNOYDELAY 60
NOLOGON disable
KILLDELAY 0

NETSERVER on
NISIP 127.0.0.1
NISPORT 3551

EVENTSFILE /var/log/apcupsd.events
EVENTSFILEMAX 10

UPSCLASS standalone
UPSMODE disable

STATTIME 0
STATFILE /var/log/apcupsd.status
LOGSTATS off
DATATIME 0

The account and password work with the Website. But I got still a comlost:

apcaccess 
APC : 001,018,0458
DATE : 2017-06-13 10:29:39 +0200
HOSTNAME : bund-shutdown
VERSION : 3.14.12 (29 March 2014) debian
UPSNAME : bvg-usv001
CABLE : Ethernet Link
DRIVER : PCNET UPS Driver
UPSMODE : Stand Alone
STARTTIME: 2017-06-13 10:29:36 +0200
STATUS : COMMLOST
MBATTCHG : 5 Percent
MINTIMEL : 3 Minutes
MAXTIME : 0 Seconds
NUMXFERS : 0
TONBATT : 0 Seconds
CUMONBATT: 0 Seconds
XOFFBATT : N/A
STATFLAG : 0x05000100
END APC : 2017-06-13 14:19:25 +0200

When I test the port on bvg-usv001:

nmap -p 3052 bvg-usv001
Starting Nmap 6.47 ( http://nmap.org ) at 2017-06-13 14:23 CEST
Nmap scan report for bvg-usv001 (192.168.65.24)
Host is up (0.0063s latency).
rDNS record for 192.168.65.24: bvg-usv001.bvg.local
PORT STATE SERVICE
3052/tcp closed powerchute
MAC Address: 00:C0:B7:ED:0B:DA (American Power Conversion)
Nmap done: 1 IP address (1 host up) scanned in 0.46 seconds

I guess I've to open the port?

On the USV I tried to set the debian Server as Powerchute Client, but that didn't open the port. I doesn't do anything on the firewall 😉

Bye

Gregor

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-07-08 02:13 AM . Last Modified: ‎2024-02-29 10:13 PM

0 Likes
0
3413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:13 AM . Last Modified: ‎2024-02-29 10:13 PM

The PCNET driver relies on a passphrase rather than a password. On my AP9606 it defaults to "admin user phrase". So the driver needs to look like this :

UPSTYPE pcnet
DEVICE 192.168.2.231:apc:admin user phrase


You might want to re-check your authentication just to ensure it is set up right.

If you fire up tcpdump you should see the PCNET packets back and forwards, from memory they are plaintext anyway.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-07-08 02:13 AM . Last Modified: ‎2024-02-29 10:13 PM

0 Likes
0
3414
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 02:13 AM . Last Modified: ‎2024-02-29 10:13 PM

The PCNET driver relies on a passphrase rather than a password. On my AP9606 it defaults to "admin user phrase". So the driver needs to look like this :

UPSTYPE pcnet
DEVICE 192.168.2.231:apc:admin user phrase


You might want to re-check your authentication just to ensure it is set up right.

If you fire up tcpdump you should see the PCNET packets back and forwards, from memory they are plaintext anyway.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore