Dear all,
APC Symmetra Tm, model:SYMSTRF3I do not start even the connection is don according to " manual ". It has SYPM -power module, SYBATT -battery module ,SYMIM2 -intelligent module. There is "input power" and battery voltage ,but UPS can not turned "ON". As the UPS is not working at all, there is not any information about fault module or so . Any suggestion from you what to do nex!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:28 AM . Last Modified: 2024-03-18 12:26 AM
Did any lights on the intelligence modules come on after you got output power from maintenance bypass? You could try plugging the powerview display to the back of the unit. There is a communication card and an RJ-45 port labeled Remote PowerView. This bypasses the intelligence module.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:28 AM . Last Modified: 2024-03-18 12:26 AM
Hello Mehdi,
Sorry for the delayed response. Is the powerview display turning on? If so, what is the message you get when you go into the Control menu and attempt to turn the output power on? You said there is battery voltage--did you get that from the display or did you measure with a volt meter? What voltage are you seeing from the battery? Anything under 85 volts dc would prevent the unit from turning on. You could still force output power by flipping the maintenance bypass switch. Also make sure the System Enable switch is on and the circuit breaker on the UPS is closed.
What caused this unit to be off? Was there a power outage? Did you move the unit to a new location? Acquire the unit from someone else and you're just installing it?
-David
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:28 AM . Last Modified: 2024-03-18 12:26 AM
Hello David,
I will try to answer on some questions:
The ups display is not "working" as well.( There is no message )
I measure battery voltage with the meter on battery conductor ( back side of ups , batt voltage 115V).
I measure input voltage (three phase) on conductors in back side of ups.
This ups was not used for couple month and i try to use it in new location.
Sorry for delay!
Mehdi
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:28 AM . Last Modified: 2024-03-18 12:26 AM
Mehdi, are there any lights on the intelligence modules? On the lower left front of the unit is the Manual Bypass Switch. If you flip that the unit should pass output power. That also may get the Power View display to react. Was the unit having any issues prior to it being decommissioned?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:28 AM . Last Modified: 2024-03-18 12:26 AM
Hi David,
There is no any light coming on, on the intelligence modules when i switch the UPS on.I will try tomorrow to put on Manual Bypass Switch and to see any change. I will inform you.
best regards- Mehdi
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:28 AM . Last Modified: 2024-03-18 12:26 AM
Hi David,
I connect today again UPS and put Manual Bypass switch to" on" position. There is a voltage in the output connector. The rest of the UPS is" dead". I am very shore on that one power and one battery module are OK.
best regards-Mehdi
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 07:28 AM . Last Modified: 2024-03-18 12:26 AM
Did any lights on the intelligence modules come on after you got output power from maintenance bypass? You could try plugging the powerview display to the back of the unit. There is a communication card and an RJ-45 port labeled Remote PowerView. This bypasses the intelligence module.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-08 03:38 AM
I have same problem, Any suggestion? please