apc symmetra Tm-Power Array

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • apc symmetra Tm-Power Array
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Kepuska_apc
Crewman Kepuska_apc
Crewman

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

0 Likes
7
1484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

apc symmetra Tm-Power Array

Dear all,

APC  Symmetra Tm, model:SYMSTRF3I do not start even the connection is don according to " manual ". It has  SYPM -power module, SYBATT -battery module ,SYMIM2 -intelligent module. There is "input power" and battery  voltage ,but UPS  can not turned  "ON". As the UPS is not working at all, there is not  any information about fault module or so . Any suggestion  from you  what to do nex!  

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

0 Likes
0
1484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

Did any lights on the intelligence modules come on after you got output power from maintenance bypass? You could try plugging the powerview display to the back of the unit. There is a communication card and an RJ-45 port labeled Remote PowerView. This bypasses the intelligence module. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

0 Likes
0
1484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

Hello Mehdi,

Sorry for the delayed response. Is the powerview display turning on? If so, what is the message you get when you go into the Control menu and attempt to turn the output power on? You said there is battery voltage--did you get that from the display or did you measure with a volt meter? What voltage are you seeing from the battery? Anything under 85 volts dc would prevent the unit from turning on. You could still force output power by flipping the maintenance bypass switch. Also make sure the System Enable switch is on and the circuit breaker on the UPS is closed. 

What caused this unit to be off? Was there a power outage? Did you move the unit to a new location? Acquire the unit from someone else and you're just installing it?

-David

Reply

Link copied. Please paste this link to share this article on your social media post.

Kepuska_apc
Crewman Kepuska_apc
Crewman

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

0 Likes
0
1484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

Hello David,

I will try to answer on some questions:

The  ups display is not "working" as well.( There is no message )

I measure battery voltage with the meter on battery conductor ( back side of ups , batt voltage 115V).

I measure input voltage (three phase) on conductors in back side of ups.

This ups was not used for couple month and i try to use it in new location.

Sorry for delay!

Mehdi

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

0 Likes
0
1484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

Mehdi, are there any lights on the intelligence modules? On the lower left front of the unit is the Manual Bypass Switch. If you flip that the unit should pass output power. That also may get the Power View display to react. Was the unit having any issues prior to it being decommissioned? 

Reply

Link copied. Please paste this link to share this article on your social media post.

Kepuska_apc
Crewman Kepuska_apc
Crewman

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

0 Likes
0
1484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

Hi David,

There is no any light coming on, on the intelligence modules when i switch  the UPS on.I will try tomorrow to put on  Manual Bypass Switch and to see any change. I will inform you.

best regards- Mehdi

Reply

Link copied. Please paste this link to share this article on your social media post.

Kepuska_apc
Crewman Kepuska_apc
Crewman

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

0 Likes
0
1484
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

Hi David,

I connect today again UPS and put Manual Bypass switch to" on" position. There is a voltage in the output connector. The rest of the UPS is" dead". I am very shore on that one power and one battery module are OK.

best regards-Mehdi

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

0 Likes
0
1485
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 07:28 AM . Last Modified: ‎2024-03-18 12:26 AM

Did any lights on the intelligence modules come on after you got output power from maintenance bypass? You could try plugging the powerview display to the back of the unit. There is a communication card and an RJ-45 port labeled Remote PowerView. This bypasses the intelligence module. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Irakli
Crewman Irakli
Crewman

Posted: ‎2024-01-08 03:38 AM

0 Likes
0
688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-08 03:38 AM

I have same problem, Any suggestion? please

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of