SYMMETRA DEAD SET

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SYMMETRA DEAD SET
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Spock Teken
113
Erasmus_apc
Sisko Erasmus_apc
112
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:21 AM . Last Modified: ‎2024-03-19 01:35 AM

0 Likes
14
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:21 AM . Last Modified: ‎2024-03-19 01:35 AM

SYMMETRA DEAD SET

Hi.

Were having problem with our Symmetra Power Array Model SYMSTRF 1 after we change all the batteries of
it and we power up there is no Response from indications light and from the screen. Its all dead set....
Should we check the SYMIM or SYRIM..... Please Advise

Message was edited by: jrbaldemor

Labels
  • Labels:
  • Data Center & Facility 3 Phase UPS
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:34 AM

0 Likes
0
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:34 AM

Unfortunately, it appears the system was identified as the international chassis SYMSTRFI.

As previously discussed on this thread, despite the System Enable switch being ON, the UPS remains "dead set" when provided appropriate utility or battery power.

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 14
Anonymous user
Not applicable

Posted: ‎2021-06-26 04:21 AM . Last Modified: ‎2024-03-19 01:35 AM

0 Likes
0
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:21 AM . Last Modified: ‎2024-03-19 01:35 AM

Hi.

Were having problem with our Symmetra Power Array Model SYMSTRF 1 after we change all the batteries of
it and we power up there is no Response from indications light and from the screen. Its all dead set....
Should we check the SYMIM or SYRIM..... Please Advise

Message was edited by: jrbaldemor

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:21 AM . Last Modified: ‎2024-03-19 01:35 AM

0 Likes
0
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:21 AM . Last Modified: ‎2024-03-19 01:35 AM

Hi:

Can you specify exactly what you mean? Are there no LED's and no messages displayed on the PowerView screen? Or is getting stuck on the "Please wait" screen? or any other symptoms? Is there a load on the UPS right now?

Thanks

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:21 AM . Last Modified: ‎2024-03-19 01:35 AM

0 Likes
0
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:21 AM . Last Modified: ‎2024-03-19 01:35 AM

Hi

The UPS is totally dead set, there is no output , NO LED lights ON in the MIM and NO Display when the input ciruit breaker and System Enable are closed . The source input supply is available OK and all 3 SYPM, 4 KVA Power Modules are installed.

We investigated the I/O Module and there is a contactor switch inside but not operating when the UPS is switch on - no clicking sound. We checked that there is a black and white cable coming from the MIM Controller to the contactor coil. Possibly the contactor or controller problem, please confirm.

Based from above findings, can you advise which module is faulty, could it be the MIM/RIM or all the 3 SYPM Modules.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:21 AM . Last Modified: ‎2024-03-19 01:35 AM

0 Likes
0
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:21 AM . Last Modified: ‎2024-03-19 01:35 AM

Hi:

Keep in mind that this UPS will turn on with just a MIM. If you are having difficulty and want to confirm which module is acting up, try removing every module (batteries, power modules, RIM) except the MIM, then powering it on. Also keep in mind that sometimes the seating of these MIMs is a bit tricky. Make sure you have a solid connection and no bent pins on the MIM. If the microswitch is not engaged, the module will not turn on and thus the UPS will not turn on.

Let me know how that all goes.

Thanks

Message was edited by: CMFR

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:35 AM

0 Likes
0
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:35 AM

I'm curious to know if the SYMIM shows two green LEDs when the maintenance bypass switch is closed (enabled) with good input voltage and System Enable ON.

If you do have LEDs on the SYMIM, but nothing on the PowerView display, you may want to reseat the Symmetra Communications Card (SYCC) in the rear of the UPS (far left slot).

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:35 AM

0 Likes
0
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:35 AM

HI

The mains input is normal and when Enable Switch Button and Input Breaker is closed, there is no LED display on the Panel. We traced the I/O Module and there is a contactor that should operate and provide supply to the MIM and the Power Modules, where does the control signal come from to operate this contactor.

If the MIM is faulty will this be the symptom?

Innovator

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:35 AM

0 Likes
0
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:35 AM

With Input Breaker, System Enable, and Maintenance Bypass switches all closed/enabled, can you please answer the following?

1) Are the system fans at the bottom, front of the Symmetra spinning?
2) What LEDs are ON the Main Intelligence Module?
3) What LEDs are ON the Redundance Intelligence Module?
4) Is/Are the Network Management Card(s) powered ON in the rear of the Symmetra?

Thanks

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:35 AM

0 Likes
0
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:35 AM

Hi

There is no fan operating, NO LED Indicators are ON, it is completely deadset. If the MIM is faulty will this be the case. My guys are checking the enable switch, where is the signal coming from to start the UPS, is it an initial DC Supply to the MIM or is it AC Supply?



Innovator

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:35 AM

0 Likes
0
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:35 AM

If there is AC input into the Symmetra Power Array, and BOTH Input Circuit Breaker and Maintenance Bypass switches are both ON (up position), then the fans will spin no matter whether the System Enable is ON (up) or there is a Main Intelligence Module installed.

Since your fans are not spinning, you seem to have power issues -- possibly internal to the UPS.

Are you able to measure any voltage at the input voltage selector panel on the front-bottom of the UPS?

When was the last time this UPS was working properly? Is there any service history?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:35 AM

0 Likes
0
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:35 AM

HI

We did make measurements, from the rear incoming AC Supply and also at the rear backplane circuitboard busbar of the UPS where the MIM/RIM are connected.

We also traced the incoming power cables and bypass cables and some control signals from the top part of the module to the I/O Modules (Input and Bypass Circuit Breaker), there is a contactor switch in this module, we do not have the details of this contactor switch as the label is not too visible, do you have more information on this contactor switch or would this contactor switch be the possible problem.

We checked with the end-user on the history and they said they have a major breakdown few months ago, possibly faulty module wherein the UPS went inoperational and was switched bypass until now.

There are no more protection breakers or active components from the I/O module to the backplane of the UPS ,can you advise what values should be measured from the UPS rear busbars, it is a three phase UPS with 3 Power Module.

Looking forward to your reply.

Innovator

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2025-05-27 11:30 PM

0 Likes
0
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2025-05-27 11:30 PM

So does it appear that AC power is reaching the bus bars and passes through to output terminals while the UPS is in manual bypass? If so, you might want to check to see if perhaps the System Enable switch is malfunctioning, or perhaps the EPO is preventing the system enable from closing ON.

If you have a 3-pole input circuit breaker on the front-bottom of your Symmetra, yours is a 3ph input UPS with single-phase 230v output.

With the System Enable switch ON, and good AC power in the backplane, the SYMIM will turn on when it's microswitch is engaged. The SYMIM has its own power AC supply.

Even if the SYMIM was failed, we should assume the SYRIM is not also bad. With just a good SYMIM in the chassis, there should be signs of activity such as LEDs on the SYRIM (solid orange LED if MIM is not installed or failed), and the PowerView display would power up along with any accessory cards installed in the rear of the system.

Here is a link to the [documentation for your Symmetra if you have the 3 phase input model SYMSTRF3I|https://www.se.com/in/en/product/SY16K3I/apc-symmetra-16kva-scalable-to-16kva-n+1-380415v-31/] or if you have the [single-phase input model SYMSTRFI|https://www.se.com/in/en/product/SY16KI/apc-symmetra-16kva-scalable-to-16kva-n+1-220240v/].

You can download the user manual and installation guides if you'd like.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:34 AM

0 Likes
0
1749
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:34 AM

You identified the unit as the old solid masterfraem right away. 208 or 240 single phase. Good. The unit can actually turn on without utility power, from just salpping the SYBATTS in. Try that. Maybe you have the enable switch off instead of on. Do you have the input microswitch /config for 208 or 240? I am a little late on this thread but hope this helps. What did you do between replacing batts? Did you move the unit to another room, facility ....? Try cold start. make sure the power modules are each engaged by their latching microswitches.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:34 AM

0 Likes
0
1750
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-26 04:22 AM . Last Modified: ‎2024-03-19 01:34 AM

Unfortunately, it appears the system was identified as the international chassis SYMSTRFI.

As previously discussed on this thread, despite the System Enable switch being ON, the UPS remains "dead set" when provided appropriate utility or battery power.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Irakli
Crewman Irakli
Crewman

Posted: ‎2024-01-08 02:32 AM

0 Likes
0
1203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-08 02:32 AM

I have same problem, 

APC Symmetra Power Array Model: SYMSTRFI  

With good input voltage, good battery, UPS is not turning on, NO LED lights ON in the MIM/RIM and NO Powerview Display when the input circuit breaker and System Enable are closed (UP). Only one symptom of life, after System enable switch is closed (UP) fan of SYPM is working 20, 22 seconds and then stops. I had tried another SYPM but same. We investigated the I/O Module, it is ok.   

have anyone a idea?  please support, for me it is very important. 

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of