hi
i have a smart 1500 ups ( SUA1500I ) And ups load is 19.4 % When the electricity goes off the runtime remaining shows in powerchute is 131 min but after a few seconds the runtime becomes 70 min and continue to fall
and i've switched the battery month ago and still the same problem
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:44 PM . Last Modified: 2024-03-01 12:28 AM
You may want to try a runtime calibration to adjust this. The runtime remaining is supposed to be a "really good estimate." If there have been no full or deep discharges (or a calibration), the value may not be accurate.
You can issue the runtime calibration command via PowerChute and it will discharge the UPS down to 10-20% charge and let it charge back up. And don't worry, your attached equipment will know not to turn off. Alternatively, you can attempt a manual calibration which would require the following stepsoutlined in this article -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156538 (Note: The article covers manual runtime calibration but the topic of the article is slightly different than what you're seeing.)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:44 PM . Last Modified: 2024-03-01 12:28 AM
You may want to try a runtime calibration to adjust this. The runtime remaining is supposed to be a "really good estimate." If there have been no full or deep discharges (or a calibration), the value may not be accurate.
You can issue the runtime calibration command via PowerChute and it will discharge the UPS down to 10-20% charge and let it charge back up. And don't worry, your attached equipment will know not to turn off. Alternatively, you can attempt a manual calibration which would require the following stepsoutlined in this article -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156538 (Note: The article covers manual runtime calibration but the topic of the article is slightly different than what you're seeing.)
Link copied. Please paste this link to share this article on your social media post.