Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
apc smart 1500 Runtime issue
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0710:44 PM. Last Modified: 2024-03-0112:28 AM
apc smart 1500 Runtime issue
hi
i have a smart 1500 ups ( SUA1500I ) And ups load is 19.4 % When the electricity goes off the runtime remaining shows in powerchute is 131 min but after a few seconds the runtime becomes 70 min and continue to fall
and i've switched the battery month ago and still the same problem
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0710:44 PM. Last Modified: 2024-03-0112:28 AM
You may want to try a runtime calibration to adjust this. The runtime remaining is supposed to be a "really good estimate." If there have been no full or deep discharges (or a calibration), the value may not be accurate.
You can issue the runtime calibration command via PowerChute and it will discharge the UPS down to 10-20% charge and let it charge back up. And don't worry, your attached equipment will know not to turn off. Alternatively, you can attempt a manual calibration which would require the following stepsoutlined in this article -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156538 (Note: The article covers manual runtime calibration but the topic of the article is slightly different than what you're seeing.)
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0710:44 PM. Last Modified: 2024-03-0112:28 AM
You may want to try a runtime calibration to adjust this. The runtime remaining is supposed to be a "really good estimate." If there have been no full or deep discharges (or a calibration), the value may not be accurate.
You can issue the runtime calibration command via PowerChute and it will discharge the UPS down to 10-20% charge and let it charge back up. And don't worry, your attached equipment will know not to turn off. Alternatively, you can attempt a manual calibration which would require the following stepsoutlined in this article -> http://www.apc.com/support/index?page=content&country=ITB〈=en&locale=en_US&id=FA156538 (Note: The article covers manual runtime calibration but the topic of the article is slightly different than what you're seeing.)