Hi,
I am installing new UPS with 4 XLPB there is rbc1 and rbc2 but each one XLBP give error only rbc1 disconnected.
i tryed alarm test disconnect reconnect and run on UPS with no input power.
thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:43 PM . Last Modified: 2024-03-01 12:28 AM
Hello,
I asked someone about this as I was not sure. From what I understand, you've already tried to physically re-connect the internal batteries in the XLBP? If so, make sure that you have 500 watts of load or more and run a self test again. RBC's in batt packs are often not recognized without load.
If that doesn't help or change the situation, I suggest that you please contact your local technical support office as there may be a problem like a blown fuse and it may require spare parts to be sent to you which local support can handle and manage.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-07 10:43 PM . Last Modified: 2024-03-01 12:28 AM
Hello,
I asked someone about this as I was not sure. From what I understand, you've already tried to physically re-connect the internal batteries in the XLBP? If so, make sure that you have 500 watts of load or more and run a self test again. RBC's in batt packs are often not recognized without load.
If that doesn't help or change the situation, I suggest that you please contact your local technical support office as there may be a problem like a blown fuse and it may require spare parts to be sent to you which local support can handle and manage.