apc 750i switch to battery restarts pc

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • apc 750i switch to battery restarts pc
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

0 Likes
7
1095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

apc 750i switch to battery restarts pc

I have recently got an active pfc psu. I called up APC call center and asked which ups i need to go with for 400-450w load, and I am not interested in lots of backup time, allowing me to shutdown is enough. They suggested me apc 750i a pure sinewave ups. I bought it. At load my system take ~360W. At this load if power goes off, my system's off instantaneously and starts again in < 1 sec. This doesnt happen when my system is idles and takes around 180W.
I registered a complaint. They got another 750i and checked with it, same problem. Checked it with another computer , same problem at load > 350. Now if it's rated at 500W, I think it should handle atleast 350W, right? And I checked it with sensitive at low meduim and high , it's the same. When I use it with backups it works, but my psu produces buzzing sound, indicating that it's not pure sinewave. What should I do now? Go with a higher rated ups? Would apc cheange it to a higher rated ups at extra charge? Please help me, it's been over one week I bought ups and I still run my system without backup 😞

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • smart-ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

0 Likes
0
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

If possible, could you please post the data and event logs of the SUA750I to find out what is going on with it?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

0 Likes
0
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

Power consumption at load is 380W, measured by powerchute software. I have an assembled system with corsair hx620w, core i7 920 , nvidia gtx 260 benq e2200hd monitor.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

0 Likes
0
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

The SUA750I can support up to 500 Watts / 750 VA on the battery backup outlets. Please be aware that the size UPS you require depends on the load you plug into the unit. May I know the exact model number of the Computer in question? Is it Customized System or branded System?

If possible, could you please load the Power Chute software to monitor the exact equipment power consumption and the UPS run time?

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

0 Likes
0
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

What is the UPS estimated runtime showing on Power Chute software? What lights are on the front of the UPS when it restarts the Computer? I suspect that the Power Supply is not capable of handling the UPS transfer time. Typical transfer time of the Smart UPS is 4 to 6 ms. Do you have any other branded system? If so, connect it to the UPS and see if the UPS supports it. This will help us to determine the root cause of the issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

0 Likes
0
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

As I have already mentioned I have checked it with another system. coolermaster RP 600W psu. It's not a psu problem as it works well on apc back ups and two computers cant be wrong. backup time remaining is 8 min.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

0 Likes
0
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

hmm...this is odd issue. What is the model number of the Back UPS that works fine with this System?

I do not think that another replacement SUA750I will fix this issue. My suspicious is that the Server/PC in question is not able to handle the SUA750I transfer time which it takes to transfer from online to onbattery. Could you please double check if your system/PC restarts when the unit transfers from online to on battery? Are you using the Power Chute Business Edition software to monitor the Smart UPS? If you are using it, could you please post the data and event logs which was recorded when this issue occurred?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

0 Likes
0
1094
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

I have checked it many times, and with different computers. The same result. The only thing whichc matters is load. ANd yes, I am using powerchute to check load. shows 75-80% load and 7-8 minute backups remaining. It works with apc 1kva

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

0 Likes
0
1095
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

If possible, could you please post the data and event logs of the SUA750I to find out what is going on with it?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore