Repetitive Power Failed / Power Restored Emails

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Repetitive Power Failed / Power Restored Emails
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

0 Likes
10
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

Repetitive Power Failed / Power Restored Emails

I have had 2 APC Smart UPS 1500 VA 980 Watt Rack Mount units in our office for about a year. Ever since we installed them we will get occassional "Power Failed on Agent xxx" followed immediately by "Power Restored on Agent xxx" emails. I often see the restored email arive before the failed ones.

Some times this will go on for 10 minutes or more with 5 or 10 emails a minute. Other times it will happen once, and then again 10 or 30 minutes later... just constantly causing a worry that something is wrong with the System and it is about to go down. Sometimes one of the UPS units will report the outage, sometimes the other.

I sit less than 15 feet from the server and there is never the slightest indication that the power has flickerd.

On the rare occassion we will get a email stating that there was a site wiring fault, and I suspect that it could be part of the problem... .but what is indicated by the UPS saying the power has failed, when it obviously is still flowing.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Taomyn_apc
Crewman Taomyn_apc
Crewman

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

I just purchased an SMT1000I to replace an older SMART-UPS and I am experiencing this issue, again! I say again, because I used serial before and thought that when I got this brand new unit APC might have actually got around to fixing this issue, that I would switch to USB. I obviously overestimated their abilities and wish I hadn't.

Why on a 2010/2011 piece of hardware is this error still happening? I don't buy the "interference" excuse as USB is a protocol not a dumb connection, plus I the only other USB device plugged in is my keyboard so it's hardly going to be taxing the bus.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

Randy,

Have you checked the UPS data logs to see if there were short power failures when you received these emails alerts? The data logs show you the input voltage that the UPS received. Check if there was any short blackouts that triggered these alerts.

If possible, could you please post the data and event logs which was recorded during the email alerts? May I know the version of the Power Chute software? Are you using the Serial cable or USB cable?

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

I do not see any blackouts in the data logs. Unfortunately, I am not able to open the event logs which you posted for some reason. Could you please re-post the event logs same as the data logs?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

Hi Randy,

Are you using a USB cable to connect your UPS into the computer? If you do, would it be possible for you to change it to serial? The problem that you are experiencing might be related to communication issue. Please do let us know what kind of cable you are using.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

Yes, I'm using USB for both. It is logging these as events as well, would it do that if there was a USB issue?

I'll have to see if I have serial cords/ports and take some time to make that change if other items don't work out.

Thanks,
Randy

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:25 AM

Randy,

If you have multiple USB devices connected on the computer where the UPS is also plugged in they tend to collide with the data that our UPS is sending. We are using USB1.1 on our UPS and as you may already know USB devices now are on the USB2.0 which is much more faster that what we use. Also, if you are using a USB hub to connect the UPS to the computer, please try to plug the UPS directly into the USB port of the computer.

Please be informed as well that you need to use the APC serial cables with part numbers 940-0024 or 940-1524, if you connect non-APC cables this can cause your server to drop its load. Prior to changing the cables you need to braindead the Smart-UPS, I've listed the steps below we need to do this to disable the USB function of the UPS.

- Turn off the equipment that is connected to the UPS
- Disconnect the UPS from is AC (input power) source
- Press the Off button to turn the UPS off and release it.
- Press and hold the Off button for approximately five seconds to turn off the DC (battery) power. You may hear the unit click and flash its front LEDs.

After doing the braindead procedure you may now connect the APC serial cable and you also need to uninstall and reinstall the PowerChute Business Edition software on your PC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:24 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:24 AM

Thanks for the screen shots. What lights are on the front of the UPS when you get these alerts? If the UPS works normally during these alerts, then this might be an erroneous report via the USB cable. APC Smart UPS SUA also ships with 940-0024/1524 serial cable. Please try connecting the serial cable(940-0024/1524) and check if the issue lies with the USB cable or some other thing.

Message was edited by: Techie

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:24 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:24 AM

It is hard to tell what the lights are doing when I get the email after it is over...

On some occassions I do see the lights acting odd as well. I'll watch for it, and see if I can see something change when it is particularly active.

The procedure for changing the UPS to serial seems quite invasive. I will have to schedule some time to take the servers down to switch.

Honestly, we have had more outages from having a UPS than we would have if we never purchased it at this point it has cost us a fair amount of time and worry and productivity, exactly the thing we bought them to avoid.

Reply

Link copied. Please paste this link to share this article on your social media post.

Techie_apc
Sisko Techie_apc
Sisko

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:24 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:24 AM

Randy,

I understand what you are going through. Please go through this troubleshooting exercise to find the root cause.

Have a nice day!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:24 AM

0 Likes
0
1645
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:31 PM . Last Modified: ‎2024-03-14 04:24 AM

Please keep us updated with the problem and what have you done so far. We will do our best to help you with it.

I am sorry for the inconvenience this has caused you. Please feel free to contact APC Customer Care Center if you are not comfortable doing the braindead procedure by yourself. Our center is open Mondays to Fridays from 8:00AM until 8:00PM Eastern Time.

Reply

Link copied. Please paste this link to share this article on your social media post.

Taomyn_apc
Crewman Taomyn_apc
Crewman

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:32 PM . Last Modified: ‎2024-03-14 04:24 AM

I just purchased an SMT1000I to replace an older SMART-UPS and I am experiencing this issue, again! I say again, because I used serial before and thought that when I got this brand new unit APC might have actually got around to fixing this issue, that I would switch to USB. I obviously overestimated their abilities and wish I hadn't.

Why on a 2010/2011 piece of hardware is this error still happening? I don't buy the "interference" excuse as USB is a protocol not a dumb connection, plus I the only other USB device plugged in is my keyboard so it's hardly going to be taxing the bus.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore