I can connect to the card via a serial port with hyperterm.
See below the mac address is all zeros.
Does the A- mean there is an error with one of the bin files?
User Name : apc
Password : ***
American Power Conversion Network Management Card AOS v6.0.6
(c) Copyright 2012 All Rights Reserved Smart-UPS & Matrix-UPS APP v6.0.6
-------------------------------------------------------------------------------
Name : apcnew01 Date : 02/10/2007
Contact : Unknown Time : 09:54:31
Location : Unknown User : Super User
Up Time : 0 Days 0 Hours 3 Minutes Stat : P+ N4- A-
Type ? for command listing
Use tcpip command for IP address(-i), subnet(-s), and gateway(-g)
apc>
Active IPv4 Settings
--------------------
Active IPv4 Address: 0.0.0.0
Active IPv4 Subnet Mask: 0.0.0.0
Active IPv4 Gateway: 0.0.0.0
Manually Configured IPv4 Settings
---------------------------------
IPv4: enabled
Manual Settings: enabled
IPv4 Address: 192.168.2.44
Subnet Mask: 255.255.255.0
Gateway: 192.168.2.1
MAC Address: 00 00 00 00 00 00
Domain Name: example.com
Host Name: apcnew01
apc>
apc>about
E000: Success
Hardware Factory
---------------
Model Number:
Serial Number:
Hardware Revision:
Manufacture Date: 02/09/2007
MAC Address: 00 00 00 00 00 00
Management Uptime: 0 Days 0 Hours 4 Minutes
Application Module
---------------
Name: sumx
Version: v6.0.6
Date: Apr 5 2013
Time: 11:25:39
APC OS(AOS)
---------------
Name: aos
Version: v6.0.6
Date: Apr 5 2013
Time: 10:36:37
APC Boot Monitor
---------------
Name: bootmon
Version: v1.0.2
Date: Jan 21 2010
Time: 13:35:57
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:16 AM . Last Modified: 2024-02-14 11:21 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:16 AM . Last Modified: 2024-02-14 11:21 PM
Hello, im facing the same problem, did u find a solution??
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:16 AM . Last Modified: 2024-02-14 11:21 PM
Hi,
"A-" in the stat section refers to the application file - the firmware file that tells the NMC what type of unit it is installed in - has failed to load for some reason. If the application does not load, you would still be able to connect to the NMC via telnet/FTP, and still be able to pull up a webpage from the IP address, but no information would be present. If this occurs, rebooting the card will cause the application to attempt to reload. If the issue is still not resolved, it may be necessary to reflash the firmware of the device.
See Knowledge Base document FA156047 for assistance with flashing the firmware.
You should upgrade to firmware 6.4 when flashing the firmware to get the card up to the latest version.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:16 AM . Last Modified: 2024-02-14 11:21 PM
Since the MAC address is all 00 00 00 00 00 00, the NMC needs to be replaced and fixing the firmware won't help with that problem. The user cannot re-program the MAC as this is done in the factory. In addition, all of the factory information appears to be missing - model number, serial number, etc.
The card looks to be kind of old. Did you just purchase it from some place new or is it used? Does it have a sticker on it physically with a model, serial number, and MAC? The manufacturing date itself seems earlier than when the product was released so I am curious as to the history on the card and where it came from.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:16 AM . Last Modified: 2024-02-14 11:21 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:16 AM . Last Modified: 2024-02-14 11:21 PM
Angela,
There are stickers on the bottom of the card here is the info. It is a used card. Took several attempts to reset the card/password.
00 C0 B7 C7 0D 36 | AP9630 | ZA1018023732 |
From the BM> screen
BM>mfginfo
======== Mfg Information ========
CRC = FAIL
MAC Address : ???
Model : ???
HW Rev : ???
Serial Number: ???
Date of Mfg. : ???
International: 0
Language : 0
=================================
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:16 AM . Last Modified: 2024-02-14 11:21 PM
Hi John,
It seems at some point the card itself has lost its programming including MAC, model, serial number, etc. The missing MAC will prevent this NMC from working properly on a network while the other things being missing you could probably get away with. Unfortunately, this NMC needs to be replaced and I'd put it aside and pursue getting another one on your end.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:16 AM . Last Modified: 2024-02-14 11:21 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:16 AM . Last Modified: 2024-02-14 11:21 PM
Angela,
I was able to upgrade the card firmware to v6.4.0, NO crc errors anymore
see below:
-----------------
BM>sysinfo
Model : ???
MAC Address : ???
Serial Number: ???
CPU Speed : 200
Link Port : 3
Warmstart : NO NMI Count: 0
*********** FLASH MODULE INFORMATION *****************
Boot Monitor :
Name : apc_hw05_bootm Build Date : Apr 8 2014
Header Crc : A9D5(PASS)
Module Crc : 9897(PASS)
AOS :
Name : apc_hw05_aos_640.bin
Version : 640
Cookie : 963201
Build Date : Dec 18 2015
Header Crc : 5709(PASS)
Module Crc : 2D6A(PASS)
APP :
Name : apc_hw05_sumx_640.bin
Version : 640
Cookie : 963201
Build Date : Dec 18 2015
Header Crc : 4F84(PASS)
Module Crc : DD2F(PASS)
MTO : Not Present
LPK : Not Present
BM>apc>system
E000: Success
Host Name Sync: Disabled
Name: apc000000
Contact: Unknown
Location: Unknown
Message:
DateTime: 02/09/2007:12:32:26
User: apc
Up Time: 0 Days 0 Hours 10 Minutes
Stat: P+ N- A+
Bootmon: bootmon:v1.0.8
AOS: aos:v6.4.0
App: sumx:v6.4.0
apc>about
E000: Success
Hardware Factory
---------------
Model Number:
Serial Number:
Hardware Revision:
Manufacture Date: 02/09/2007
MAC Address: 00 00 00 00 00 00
Management Uptime: 0 Days 0 Hours 10 Minutes
Application Module
---------------
Name: sumx
Version: v6.4.0
Date: Dec 18 2015
Time: 15:14:26
APC OS(AOS)
---------------
Name: aos
Version: v6.4.0
Date: Dec 18 2015
Time: 15:04:27
APC Boot Monitor
---------------
Name: bootmon
Version: v1.0.8
Date: Apr 8 2014
Time: 10:59:40
apc>
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:16 AM . Last Modified: 2024-02-14 11:21 PM
Hi John,
What method did you upgrade it by? I don't see how the card will work properly on a network or retain TCP/IP settings with no MAC programmed in, even after upgrading.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:16 AM . Last Modified: 2024-02-14 11:21 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-09 03:16 AM . Last Modified: 2024-02-14 11:21 PM
Hello, im facing the same problem, did u find a solution??