Managment console can not found UPS, Also LED indicate "Comm Event: message

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Managment console can not found UPS, Also LED indicate "Comm Event: message
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

0 Likes
9
3421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

Managment console can not found UPS, Also LED indicate "Comm Event: message

It is Smart-UPS SRT 5000. Model Number is AP9537SUM.

1. We lost connection between the management interface and the UPS. It was working till yesterday.

2. The management web gui said "No UPS Found".

3. The UPS LED showed the attached message "Comm Event" 

4. We did upgrade the management firmware version to APS OS v6.4.0

5. Also we tried to tune it off by the front menu on UPS. Immediately shutdown ... and press OK but nothing happened.

1. Is the UPS unit bad? Need to replace?

2. How can we troubleshoot next? Unplug the power input and battery input?

 

LED message

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

0 Likes
0
3420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

HI Angle,

We got the same situation of this case. we followed the related action you recommend, then the problem solved, but after a month, that error was happen again, ...is there any environment problem related? 

BOB

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
Anonymous user
Not applicable

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

0 Likes
0
3420
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

---Sorry correction

4. We did upgrade the management firmware version to APS OS v6.4.0. But it didn't fix the problem.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

0 Likes
0
3424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

Can you share a screenshot from the web interface of About->Network menu? There are a few variants of AOS 6.4.0 so I just want to ensure to start you downloaded and applied the correct one. If you can get the About->Support logs (you need to press Generate Logs, then download Logs) those would be helpful too.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

0 Likes
0
3424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

Thanks Toshi! I think there may be an internal communication fault with the UPS. Everything in the management interface looks okay to me based on the screenshot and the logs you gave me. I can see that the management interface isn't "talking" to the UPS intelligence.

I did a little research and from what I see, it is suggested that you try to "brain dead" the UPS if you're able to. It involves removing everything connected to the rear of the UPS (power and data cables) - meaning you'd have to turn off any attached load or equipment first. Then, remove AC input power to the UPS (remove input power cord or trip input or upstream breaker), and lastly, remove/disconnect the batteries from the unit. You may have to hold down the power button for 5 seconds or so with all of that stuff disconnected. You can let it sit for a few minutes like this and the intelligence should reset. Then, I'd reconnect the batteries, restore AC power, and see if you can get the UPS to come on. Tech support can also guide you through this if you wanted.

If this does not work, I'd suggest sending the picture of the front panel on the UPS along with the screenshot and logs I asked you for to our technical support team who you can also provide this thread to. You can use esupport@apcc.com or call 800-800-4272 if you want to talk on the phone. Once they confirm some steps and other details with you, then I think they can make a decision on warranty replacement or other potential fixes.

Hope this guidance helps you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

0 Likes
0
3424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

Hi Angela,

Thank you so much! It is resolved by your advice. I followed your "brain dead" procedure and the UPS came back online with healthy status.

 

Best,

Toshi

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

0 Likes
0
3424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

Glad I could help cool If it happens again, then I'd probably see if it clears again but still notify tech support that it keeps happening and see what they can do.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

0 Likes
0
3421
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

HI Angle,

We got the same situation of this case. we followed the related action you recommend, then the problem solved, but after a month, that error was happen again, ...is there any environment problem related? 

BOB

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

0 Likes
0
3424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

Same problem here with SRT2200RMXLI 

Display is red.

What is causing this problem? Is there any protection while screen is red?

Just got the new unit and this happened after 3 weeks.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

0 Likes
0
3424
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 04:54 AM . Last Modified: ‎2024-03-18 04:00 AM

HI Yo,

any update of it? please advise. thanks 

Bob

Reply

Link copied. Please paste this link to share this article on your social media post.

tdang
tdang
Cadet

Posted: ‎2025-03-14 06:45 AM

0 Likes
0
260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-14 06:45 AM

I know old topic, we but just ran into same issue. Anything that can be done to fix, or does UPS need to be replaced?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of