Wrong firmware installed
Hi all,
I installed the wrong firmware on the NMC and it has lost connection to the UPS. Is there any way to recover? Web interface works and can finally be used with a modern browser ...
UPS: Smart-UPS RT 5000XL
NMC: AP9631
Firmware installed: apc_hw05_aos650_sy3p650_bootmon108.exe
This is the problem - firmware is for Symmetra 3-Phase, not Smart. I was led astray by the "Firmware Upgrades for all supported APC offers" tag line. My understanding is, I need the sumx application module.
apc>about
E000: Success
Hardware Factory
---------------
Model Number: AP9631
Serial Number: 5A1210T09330
Hardware Revision: 05
Manufacture Date: 03/11/2012
MAC Address: 00 C0 B7 93 DF 03
Management Uptime: 0 Days 1 Hour 2 Minutes
Application Module
---------------
Name: sy3p
Version: v6.5.0
Date: Jul 12 2017
Time: 19:00:54
APC OS(AOS)
---------------
Name: aos
Version: v6.5.0
Date: Jun 9 2017
Time: 13:41:00
APC Boot Monitor
---------------
Name: bootmon
Version: v1.0.8
Date: Apr 8 2014
Time: 10:59:40
apc>
Thanks, Larry
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:30 AM . Last Modified: 2024-03-07 11:00 PM
Hi,
You can download the proper firmware from this link.
If the firmware cannot be uploaded to the NMC using the wizard you will find instruction on how to upload manually in Schneider Electric FAQ FA156047
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:30 AM . Last Modified: 2024-03-07 11:00 PM
Hi,
You can download the proper firmware from this link.
If the firmware cannot be uploaded to the NMC using the wizard you will find instruction on how to upload manually in Schneider Electric FAQ FA156047
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-30 07:30 AM . Last Modified: 2024-03-07 11:00 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:30 AM . Last Modified: 2024-03-07 11:00 PM
Thank you, Bill. Update via wizard worked and UPS is fully accessible again!
I'm just surprised I wasn't able to find the version you linked to. Maybe it's a location thing, I see your link is pointing to us/en/products.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-30 07:31 AM . Last Modified: 2024-03-07 11:00 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:31 AM . Last Modified: 2024-03-07 11:00 PM
I also can't find any firmware for SRT5KRMXLI with AP9537SUM NMC. Changing location on the search page doesn't seem to have any impact.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:31 AM . Last Modified: 2024-03-07 11:00 PM
Hi,
It is the same firmware for the AP9537SUM as the AP9631.
Ebr1ywZ7LZPxRDgmXwlUmw%3D%3D.png
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-30 07:31 AM . Last Modified: 2024-03-07 11:00 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 07:31 AM . Last Modified: 2024-03-07 11:00 PM
Got it. Thanks!