SMX1500RM2U 12V output?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMX1500RM2U 12V output?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 07:31 AM . Last Modified: ‎2024-03-07 11:00 PM

0 Likes
3
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:31 AM . Last Modified: ‎2024-03-07 11:00 PM

SMX1500RM2U 12V output?

Hello! 

I have an APC SMX1500RM2U UPS. It's time for me to replace the batteries, and I'm in the process of doing that. At the same time, I noticed a majority of the components I'm powering are actually 12V DC devices. Since the UPS is well past it's warranty, and I'm an electrical engineer, I'd like to bypass the UPS's AC outlets and connect my devices through a fuse -- and possibly an efficient voltage regulator circuit -- directly to the devices, instead of going AC->DC->AC->DC and incurring so many power losses. My question is, is there already a 12V regulator circuit I could tap into in the UPS? Perhaps going into the interverter circuit? And/or perhaps if someone has a schematic of this UPS? Option B would be I just hunt for it on my own with a meter, Option C install my own regulator. Option C is easy, but I thought I'd just check to see if anyone has crossed this bridge before... 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-30 07:31 AM . Last Modified: ‎2024-03-07 11:00 PM

0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:31 AM . Last Modified: ‎2024-03-07 11:00 PM

Ahh, I missed the "X" in the part number. Yeah, 48V.

I've done a stack of tests on 48V banks hooked up to SU and SUA series UPS. Invariably by the time the batteries start to drift out of balance they are really near end of life. I have 2 identical units, both with 17Ah internals and 55Ah of externals. I left one on its own, and the other I manually applied an equalizing charge once a month. The batteries didn't last much longer (maybe a couple of months) from a roughly 5 year life. It was a long and ultimately fruitless experiment.

If you buy quality batteries and they all live in the same environment they do tend to age fairly well together. An in principle, you have 24 cells. You'd only be balancing them in bunches of 6, so you still have the potential for drift within each set of cells.

The key for longer life seems to be to make sure they are run toward the bottom of the float voltage spec.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-30 07:31 AM . Last Modified: ‎2024-03-07 11:00 PM

0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:31 AM . Last Modified: ‎2024-03-07 11:00 PM

Option C is your only realistic option, but not at all optimal. There is a 12V rail in the UPS that is generated from a little flyback DC/DC converter, but it's not going to sustain anywhere near the sort of load you are after (more than perhaps an extra 100mA).

You would need to build your own 24->12V DC to DC converter and at that point you are simply using the UPS as an expensive and relatively inefficient 24V float charger.

If you were to do that, any potential runtime estimates by the UPS on the 240V output would be out the window, so you compromise that also. The Charger is relatively limited in the current it can provide as it's entire purpose is to charge and maintain a battery. Sustained charge current is going to be a couple of amps at best. Additionally, you lose the low voltage protection, so you'd need something to prevent deep discharging the SLAs and the consequential impact on service life.

If it were me, I'd be picking up a bigger 12V SLA and equipping it with a float charger big enough to run the desired load, with a couple of amps left to charge the battery after a big outage and an undervoltage cutout.

I picked up a relatively large (5A) very efficient SMPS, put that on the UPS output and ran all the devices off that. One power supply, more efficient and I get to power all the mains powered doodads at the same time (PoE network switches, desktop machines and so on).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 07:31 AM . Last Modified: ‎2024-03-07 11:00 PM

0 Likes
0
1354
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:31 AM . Last Modified: ‎2024-03-07 11:00 PM

You're right! I realized after this post that the 4 SLA Batteries are wired in series for 48V so I would have to go even further to pull off 24V out of half that, and probably hook up a battery equalizer at the same time to equalize the battery draw... and probably easier to use some sort of simple charger on a timer and leave the UPS out of the mix. Why did Schneider charge the batteries in series with no equalizer circuitry? That seems really sloppy and hard on the batteries to me. I guess they were trying to avoid a complicated removable harness plug for when the batteries need to be replaced, and they consider the SLAs cost and time to replace negligible.

Full disclosure, my actual plan was to use LiFePO4 batteries so I won't have to replace them for some time, and not worry too much about deep discharge. But now I think I might just go with something simpler...

Reply

Link copied. Please paste this link to share this article on your social media post.

Brad_C
Commander Brad_C
Commander

Posted: ‎2021-06-30 07:31 AM . Last Modified: ‎2024-03-07 11:00 PM

0 Likes
0
1355
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 07:31 AM . Last Modified: ‎2024-03-07 11:00 PM

Ahh, I missed the "X" in the part number. Yeah, 48V.

I've done a stack of tests on 48V banks hooked up to SU and SUA series UPS. Invariably by the time the batteries start to drift out of balance they are really near end of life. I have 2 identical units, both with 17Ah internals and 55Ah of externals. I left one on its own, and the other I manually applied an equalizing charge once a month. The batteries didn't last much longer (maybe a couple of months) from a roughly 5 year life. It was a long and ultimately fruitless experiment.

If you buy quality batteries and they all live in the same environment they do tend to age fairly well together. An in principle, you have 24 cells. You'd only be balancing them in bunches of 6, so you still have the potential for drift within each set of cells.

The key for longer life seems to be to make sure they are run toward the bottom of the float voltage spec.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore