Why not a Windows Tray Agent in SURTA 1500XL?...

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Why not a Windows Tray Agent in SURTA 1500XL?...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

0 Likes
6
1520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

Why not a Windows Tray Agent in SURTA 1500XL?...

Hello, I have Surta 1500XL, this UPS is expensive and use it in my office with one computer attached only, could you explain me please

why there is no icon in Windows of the state of the UPS?... why the native windows power management that shows in tray how much

is left on the battery is not available when the APC  agent is installed?... Why Parachute Personal is not supported?

The web is practical for a company with some ups, but for users like my is total impractical and the worse because of the price of the

UPS I paid that is does not have the tray icon info, when are you planning to make an application that has Windows tray icon support?....

I'm starting to regret of buying a APC product and I wont recommend it either...

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

0 Likes
0
1520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

Hi,

I understand your request. I have entered an enhancement request on your behalf.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
Anonymous user
Not applicable

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

0 Likes
0
1520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

Angela, I'm part of the company and the UPS comes with the plastic bezels to remain vertical, so I wont use it in my customers closets for example, there is not message from APC that say "only for 2 or more ups, is not suited for only one ups setup"...

About business, I'm a business user and this is for my office, so there is something wrong with APC that because of this I think I wont recommend APC to my customers, the hardware could be fine but the software is really really bad.

I choose this model because I need 1500VA, at least 1.30 hours of battery for my system, the model is convenient for my office because is vertical, this model was even suggested on the UPS Selector too so I think APC has a big issue in the software side. The software that comes with the UPS has an agent for 1 ups only, again as I wrote before, the hardware could be fine but the software is very very bad for the price I paid, Cheaper UPS's has better software than this.

For the other side, if its business oriented, the software should manage encrypted smtp and selection of ports that does not have, it is not even suited for business use too...

I regret buying this ups...

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

0 Likes
0
1520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

Hi,

The SURTA should have a USB port. If you do not want to use PowerChute Business Edition you can configure Windows native shutdown (see Kbase FA159653) that provides the power icon. Another option is to install APCUPSD that offers a power icon and the ability to power down multiple systems.

If you have installed PowerChute and switch back to native power options you may need to re-enable the HID UPS driver. Kbase FA159743 discusses how to switch drivers.

As for the issue with SMTP ports, we are aware of the frustration and this will be address in a future release.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

0 Likes
0
1520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

Hello, of course I have connected the USB, if I a have Windows native power management I get the icon with the battery like in a laptop but I dont get the statistics and the email notifications, if I install the Parachute business I get the notifications but I dont get the tray icon like in Windows, I need both worlds, Parachute Business with the tray icon like in Windows because when you work on the system and there is a black out, is not possible to check every time the lights in the UPS because sometime you have to analyze the battery time remaining to finish or not the customer  project, is not possible that I need to go to Firefox to check this. Notifications are useful to control the state of the electricity network when we are out of the office with the customers and we connect to the system by remote, so in case of black out we have realtime feedback to see if we continue to work or not.

I'm not a home user that I need the ups to last till I shutdown my computer, I work for different companies in IT security, I can not have a sudden shutdown loosing my work and I don't have time (I dont like to do it too) to monitor every time the battery charge.

I dont know if its clear my point.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

0 Likes
0
1520
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

Smart-UPS UPSs are geared towards network closets and server rooms and not really the home user even though some "power users" like to use them for offices and desktop computers like yourself. PowerChute Personal Edition is supported by Back-UPS products via USB which are the product lines geared towards home users and consumers.

Smart UPS utilize PowerChute Business Edition and the software says it - it is marketed towards business users who have these plugged into servers in racks usually supporting servers that are not typically occupied by a user. It supports both serial and USBs for the aforementioned users and environment. Your UPS happens to only support serial I believe (*Edit* As noted below, the smaller VA SURT units support USB). Unfortunately, I just think your application and requirements spreads across two product line offerings from APC or else you could've maybe went with a Back-UPS. I am not sure why you chose a higher end online Smart-UPS? Was it required for your equipment?

And I can't speak for Windows native OS, it appears to not care what type of UPS you have and just works the same way no matter what unlike our two different versions of software we offer.

I don't think they are looking at adding a Windows tray icon for this based on what I mentioned but that is an educated guess. Please don't shoot the messenger smile

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

0 Likes
0
1521
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

Hi,

I understand your request. I have entered an enhancement request on your behalf.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

0 Likes
0
1522
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 05:55 AM . Last Modified: ‎2024-03-05 12:05 AM

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore