Why does my UPS switch off without warning?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Why does my UPS switch off without warning?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
perrorist_apc
Ensign perrorist_apc
Ensign

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:54 AM

0 Likes
17
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:54 AM

Why does my UPS switch off without warning?

I have a 9-year old SUA 1500I UPS that reports no problems. However, without warning, it emits a blip sound and then switches off. I can switch it back on but I've no idea why it turned off. I now feel like my UPS needs its own UPS.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:41 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1574
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:41 AM . Last Modified: ‎2024-03-12 02:53 AM

What "monitor" specifically are you talking about? PowerChute or something else?

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 17
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1574
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

My first thought is maybe the battery is faulty and when the UPS wants to go to battery for a particular reason very quickly, it is turning off. (FYI: Reasons a Smart-UPS Will Transfer to Battery | FAQs | Schneider Electric US)

How old is the battery? Also, when you go to turn it back on, are there any LEDs on the front panel? And when you turn it on, does the UPS run through its short on battery self test?

If it were me, I'd do a pull plug test and start with seeing how it behaves. Plug a non critical load into the UPS and make sure to remove any USB/serial cables that can interfere in the UPS shutdown behavior. Then, pull the UPS plug from the wall to simulate a power event and see what it does. If it turns off, I tend to blame the battery assuming it is not brand new, but if the UPS is passing the self test when you power it on, that may not be the case.

Reply

Link copied. Please paste this link to share this article on your social media post.

perrorist_apc
Ensign perrorist_apc
Ensign

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

The battery was installed in January 2012, so it's probably not far off needing replacement. I suspect you're right about the self-test, as it occurred around the time the self-test usually kicks off.

When I switched the power back on, all five charge lights came on (96%) and the self-test completed without complaint. No other lights are showing.

In the past, when the battery has begun to lose capacity, it's been reflected in shorter backup times rather than turning itself off.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

Hmm, it still could be a UPS issue of some type, especially since it passes the self test. Did you try the pull plug test?

Also, it could be something like a relay weld but this usually displays some type of solid/flashing LED combination to indicate a failure mode when the UPS would turn off.

Reply

Link copied. Please paste this link to share this article on your social media post.

perrorist_apc
Ensign perrorist_apc
Ensign

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

Yes, I pulled the plug out and it switched immediately to backup. After a minute I plugged it back in. Charge was four lights out of five for a few minutes, before returning to fully charged.

Is it possible that a malfunctioning attached device could cause the problem?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

It could I suppose, but I don't think it is likely. Have you ever seen your UPS using Automatic Voltage Regulation (boost or trim)? There are lights above and below the "online" LED that indicate this. I was wondering if it could be an issue with that relay when the UPS tries to go use AVR and fails.

Reply

Link copied. Please paste this link to share this article on your social media post.

perrorist_apc
Ensign perrorist_apc
Ensign

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

No lights. It's performed very well so far.

How long would you expect the battery to last? It's 2 years 8 months old and hasn't seen much use. It was exhausted once only.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

A battery can last anywhere from 2-5 years on average, some people get 10! It really depends on several factors - environment, build quality, use, amount of discharges/usage, etc.

Reply

Link copied. Please paste this link to share this article on your social media post.

perrorist_apc
Ensign perrorist_apc
Ensign

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

Thanks. Since that failure, the UPS has performed without any issues. I'll treat it as a one-off and hope for the best.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

Do you have a USB or serial cable attached to this UPS? I'd be interested to see if the UPS recorded a self test or if it was just an on battery event in quick succession due to electrical noise, etc. Sometimes a faulty serial cable connected can cause this too is why I ask.

How much load is on the UPS? (Left bar graph)

Reply

Link copied. Please paste this link to share this article on your social media post.

perrorist_apc
Ensign perrorist_apc
Ensign

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

I think this must be related to my original post:

This morning I heard the UPS switch self-test three or four times in quick succession. I looked at the panel and saw that the charge lights were set at the lowest (one light, which flashed briefly). No other lights were displayed. Gradually, the battery increased its charged state to 100%.

Is it possible for the unit to flash discharge the battery? Is this indicative of an electrical short? The unit is running normally again, but I can't help wondering when the next event will occur.

Reply

Link copied. Please paste this link to share this article on your social media post.

perrorist_apc
Ensign perrorist_apc
Ensign

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

No connection, but perhaps I should. I'll get back to you on the load.

Reply

Link copied. Please paste this link to share this article on your social media post.

perrorist_apc
Ensign perrorist_apc
Ensign

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

Powerchute Business Edition, latest version, running under Windows 8.1 Pro x64.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

Hi,

PowerChute should not be using 25% of the CPU. Is the UPS connected via USB or Serial? Would you share the log file(s) all files under Program Files\APC\PowerChute Business Edition\agent\log and Program Files\APC\PowerChute Business Edition\agent\proclog.txt.

I have added you as a friend so you can send the logs to me directly instead of posting them.

Thanks,

Reply

Link copied. Please paste this link to share this article on your social media post.

perrorist_apc
Ensign perrorist_apc
Ensign

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:40 AM . Last Modified: ‎2024-03-12 02:53 AM

As mentioned in my email to you, the process is running now using negligible resources following a system reboot.

Reply

Link copied. Please paste this link to share this article on your social media post.

perrorist_apc
Ensign perrorist_apc
Ensign

Posted: ‎2021-06-29 08:41 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:41 AM . Last Modified: ‎2024-03-12 02:53 AM

It's reporting 9.7% UPS Load.

Reply

Link copied. Please paste this link to share this article on your social media post.

perrorist_apc
Ensign perrorist_apc
Ensign

Posted: ‎2021-06-29 08:41 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1576
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:41 AM . Last Modified: ‎2024-03-12 02:53 AM

It's now risen to 15.6% and stayed there.

BTW, why does the monitor take up so much CPU. It's showing 25% all the time.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:41 AM . Last Modified: ‎2024-03-12 02:53 AM

0 Likes
0
1575
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:41 AM . Last Modified: ‎2024-03-12 02:53 AM

What "monitor" specifically are you talking about? PowerChute or something else?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of