Which battery should I replace? Smart-UPS VT 40 kVA

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Which battery should I replace? Smart-UPS VT 40 kVA
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

0 Likes
3
1669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

Which battery should I replace? Smart-UPS VT 40 kVA

Hi,

My company has a Smart-UPS VT 40 kVA and this morning it started reporting a failed battery. There are 16 batteries in the device and I was just wondering how I would go about finding the faulty one, short of pulling them all out one by one until the error disappears.

The device is networked so I can get into the web config however I can't find anything that would tell me exactly which battery is faulty. Would I have to use a volt meter maybe? All I can find in the user manual is that the batteries are hot swappable.

If anyone knows the procedure I should follow please, it would be greatly appreciated.

Many Thanks,

James

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

0 Likes
0
1669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

You are actually right with your post, remove rows of batteries until the fault goes away and then you know which row of batteries the faulty on is in.

The SUVT does not have the individual battery monitoring reporting like the larger Symmetra PX or small LX systems do.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

0 Likes
0
1669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

Hi Kewster, for a UPS as large as this I would probably recommend calling in to tech support at 1 800 800 4272 option 5 for tech support and speak with one of the 3 phase techs to walk you though the proper procedure.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

0 Likes
0
1669
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

hello,

The Vt is built up as a matrix, go under menu, fault and diag and it will tell where is the damage. keep in mind that you have to replace two battery module even if one is faulty.check for the right configuration in the user manual
Hope I could help. if there is anything else.....

M

Reply

Link copied. Please paste this link to share this article on your social media post.

upsguy_apc
Commander upsguy_apc
Commander

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

0 Likes
0
1670
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

You are actually right with your post, remove rows of batteries until the fault goes away and then you know which row of batteries the faulty on is in.

The SUVT does not have the individual battery monitoring reporting like the larger Symmetra PX or small LX systems do.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore