Smart-UPS RT 6000 XL - Recent warnings

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS RT 6000 XL - Recent warnings
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

0 Likes
5
1747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

Smart-UPS RT 6000 XL - Recent warnings

Greetings,

One of our UPS's, the Smart-UPS RT 6000 XL, since today morning, ( 09/01/2012) , started to write these warnings in the log file:

09.01.2012 09:44:16 UPS: A discharged battery condition no longer exists.
09.01.2012 09:44:16 UPS: The load exceeds 100% of rated capacity.
09.01.2012 09:44:16 UPS: In bypass in response to an internal hardware fault.
09.01.2012 09:43:28 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately

and also these:

09.01.2012 09:58:38 UPS: A discharged battery condition no longer exists.
09.01.2012 09:58:38 UPS: The load exceeds 100% of rated capacity.
09.01.2012 09:58:38 UPS: In bypass in response to an internal hardware fault.
09.01.2012 09:57:30 UPS: The battery power is too low to support the load; if power fails, the UPS will be shut down immediately.
09.01.2012 09:54:52 Environment: A fault no longer exists for integrated Environmental Monitor Output Relay (Int Relay at Int Relay Location).
09.01.2012 09:54:48 UPS: The load no longer exceeds 100% of rated capacity.
09.01.2012 09:54:47 UPS: No longer in bypass.
09.01.2012 09:54:21 Environment: A fault exists for integrated Environmental Monitor Output Relay (Int Relay at Int Relay Location).


In the afternoon:

09.01.2012 14:30:15 UPS: Passed a self-test.
09.01.2012 14:30:00 UPS: Started a self-test.

In the main page, I don't see any alarm (See attached file) . So I'm a little worried if the battery is gone bad.
Any help is appreciated

Cheers

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

0 Likes
0
1745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

637/5000
Good day, I have a similar problem and I do not know what the cause is, I have the following log:

The UPS works normally. There are no alarms.

UPS is online.



Recent events of the device
Date Time Event
03/26/2018 09:24:41 UPS: Passed a self-test.
03/26/2018 09:24:25 UPS: Started a self-test.
03/23/2018 17:01:33 UPS: a discharged battery condition no longer exists.
03/23/2018 17:01:30 UPS: the battery power is too low to withstand the charge; If the power fails, the UPS will shut down immediately.
03/23/2018 16:56:41 UPS: a discharged battery condition no longer exists.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

0 Likes
0
1745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

hello,

in order for us to better analyze, can you get us config.ini, data.txt, and event.txt from the network management card? directions are here -> http://nam-en.apc.com/app/answers/detail/a_id/9321

thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

0 Likes
0
1747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

Thank you kindly for your fast reply.
Attached files as requested.

Cheers

" Edited: Sorry. The config.ini and data.txt contain some confidential network information. Is there any other way to let you check those logs"? Email maybe?
Cheers

Message was edited by: sandroasantos

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

0 Likes
0
1747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

yes, i will PM you my email and you can email them.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

0 Likes
0
1747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

ok, i have your logs. what i am seeing is that the data log is recording large rises in % wattage out. can you let me know what you have attached to the UPS? is there something that powers on/off once in a while that has a large in rush of current? or that is attached to the UPS output and you are unaware? also, if you have PDUs attached (power strip type) maybe someone is coming in and uses those outlets unknowingly. it seems to be happeneing each day around 9:45 and maybe other random times.

i think the UPS keeps getting overloaded and because of this, it goes to bypass because the load is greater than 100% for a certain amount of seconds.

i think the first step is to investigate what is connected and what can be turning on between 9-10am. see if you find anything there. i see no reason why this alarm is not legitimate.

i also think you have an overload or bypass fault that is mapped to activate the environmental relay? I am referring to: Environment: A fault no longer exists for integrated Environmental Monitor Output Relay (Int Relay at Int Relay Location).

i verified that in your config.ini OutputRelaySwitchMapping1=enabled:onBat,lowBat,badBat,lostComm,noOutVolt,overLoad,inBypass,fault so that's why that is coming up.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

0 Likes
0
1746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 01:23 AM . Last Modified: ‎2024-03-11 02:40 AM

637/5000
Good day, I have a similar problem and I do not know what the cause is, I have the following log:

The UPS works normally. There are no alarms.

UPS is online.



Recent events of the device
Date Time Event
03/26/2018 09:24:41 UPS: Passed a self-test.
03/26/2018 09:24:25 UPS: Started a self-test.
03/23/2018 17:01:33 UPS: a discharged battery condition no longer exists.
03/23/2018 17:01:30 UPS: the battery power is too low to withstand the charge; If the power fails, the UPS will shut down immediately.
03/23/2018 16:56:41 UPS: a discharged battery condition no longer exists.
Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of